YORK D2CG120N20025JSB S#NFM13044---- MISSING #.
this is at Mcdonalds kitchen the lowest its get is 77*F. at 85* out door amb temp.
thermostat in the office with remote sensor in the kitchen. all exhaust fan work.
both stage reading the same Hi 245 Psi lo 65 psi compressor SH 18* R-22.
each compressor RLA 14 amp . name plate say 19.2 each stage.
cap tube with distributor metering devise.checked ducting in the attic all good.supply air 55* good air flow.
didn't check subcooling.
chemical pressured washed both coils. cleaned blower wheel.
per store manager work fine before until this summer. no renovation or anything changed to the store recently.
any idea? thanks