Whole system might be oversized

9.3K views 55 replies 10 participants last post by  dan sw fl  
#1 ·
I did a estimate of the size at 1614 square feet.

I am under the impression that my heating could be oversized as well:

Here are the Specs:

Condenser: 14acx-041
Furnace: EL180UH090e48E
evaporator coil:CH35-48B
I understand that the condenser is but what about the furnace
udarrell or ikapigan if one of you could let me know that would be great
also on scale of one to ten with 10 being the highest how damaging is this for the blower and heat exchanger
I am pretty sure you wouldn't come up with 39500 BTUs without a load calc
please not this does not take away form a load calc but gives me a ballpark value to see how oversized my equipment really is
 
#42 ·
I might I mean the rest of my people in household think the a/c is i fine. I have told them I am hot and we should call the guy. but they won't listen. I just want to be sure that the problem is not elsewhere. as far as humidity is concern it is low, all blinds are retracted so I should not feel a thing
 
#54 ·
You should record On-Off times along
with outside conditions from Noon to 7 pm
for a couple days.

Then you'll know how much oversized you are.

If your regular ON time is consistently 20 minutes in mid-afternoon
and IF _ OFF time is 10 minutes_, the system is effectively running at 66% of Peak Load.
 
Save
#49 ·
Every home should have a low cost 'INDOOR Humidity Monitor' ACU-RITE Digital only $8.94 at Walmart or over the Internet. It tells U if the humidity is in the 'OK' range, etc.
Check to see if it registers the temperature correctly; if not, take it back for a full refund.
If you want help...?
3) Outdoor condenser’s discharge-air-temperature ___°F
Subtract Outdoor air temperature: __°F
Outdoor Condenser Air-Temp-Split ___°F

4) Need the ‘Indoor’ percent of relative humidity - in the middle of the rooms or, at Return-Air inlet grilles ___%RH

5) Indoor Return Air Temperature __°F Indoor Supply-Air Temperature __°F
Subtract Indoor Supply-Air Temp from Return Air Temp __°F
Indoor temperature-split = __°F

“Reply with Quote” Fill the #numbers in where the blanks are. Easy Safe testing of your A/C or heat pump cooling performance for forum visitors to use.
 
#52 ·
ok I have a lennox merv16 filtration system right now it is performing at 50-30 percent at the no cooling loads and 60-70 at peak loads as mention the home is 1614 sq ft . the current cooling load I am at is 39500 btu or 3.2 tons which from what I understand means a 3.5 ton system. home has basic insulation and windows tend to leak a little. if there is anything else you need let me know. as far as the duct system they added some new plenum added two return grills. I am pretty sure the duct system was not don right as well
 
#53 ·
ok

I have a lennox merv16 filtration system right now it is performing at 50-30 percent at the no cooling loads and
60-70 at peak loads as mention the home is 1614 sq ft .

home has basic insulation and windows tend to leak a little.

if there is anything else you need let me know.
MERV 16 is more than likely a flow & capacity performance killer,
unless you have appropriately sized 5" thick filters.

.... 3.5 Existing Unit
X.. 70% Peak Load
2.45 Required Size
 
Save
#56 ·
SURE, I can spot any significantly abnormal values used in a calculation
in a matter of minutes given a Complete Report.

However, your best verification of
ACTUAL Heat Gains are
as addressed in COMMENT # 54 AND # 49 by U Darrell.
 
Save