Ok great refer gods, Tell me did I miss something?
W/I freezer box, been empty and down for 1 week in 100 degree plus weather.
Trashed comp wont pump, all old and rusted.
Customer said new cond unit. Evap is a Larkin ELT106 rated at 10600 btu at -10. match condensing unit with it AVA2510ZXTXC 3 Ph 404A.
New filter dryer, filled site glass, replaced txv with 1/2 to 1 ton txv.
99 degrees amb, low side 45 , high side 385, suction temp at evap 30 degrees
suction temp at comp 45 degrees, txv adjusted wide open, cant get superheat down, after 3 hours run time box temp still not below 32 degrees , box is on the outside open to enviormenet with the white rubber roof
heating elements NOT energized! Unit pumps down fine and quick!
Should have added evap only frosting 3/4 the way up!
Any inputs!
Sun has got my brain!!!!