I moved into my home back in 2018 and it had a very old outside AC unit. I had the condenser and coil replaced with a Trane 3.5 ton unit and left the gas furnace as is since that had been replaced about 5 years prior to moving in. The previous unit was a 3 ton. I did some math and determined that the old unit really wasn't sized for the whole house.
Since the new condenser and coil installation, I've had a difficult time cooling the house in the summer. Recently, I've been having even greater issues. The blower motor will kick on and off over and over again for seemingly 5-10 minutes before kicking on and blowing air through the duct. I initially thought the capacitor might be an issue, tested it and saw that it was testing well below it's rating so I replaced it. No dice, still seeing the same issue. This tends to occur mostly in the late afternoon/early evening time frame after the AC has been running nearly all day.
I'm starting to suspect the blower motor is failing and started looking into replacements. This had me dig into the service manual and I found that the blower motor is a 1/3HP motor rated for 2-3 tons of add-on cooling. I'm assuming that means that the blower motor is good for up to a 3 ton AC unit. My AC unit is 3.5 tons. I'm wondering if this is the reason they system hasn't been able to cool my house as much as I would like and also the reason why the blower motor is failing. Is it possible the the blower motor is working too hard all day to try and move that level of air and then overheating by late afternoon?
So I'm wanting to replace the blower motor and I'm thinking I ought to up-size it. The service manual shows the blower motor size for the next size up furnace from the one I have and it is a 1/2HP rated for 3-4 tons of add-on cooling. My main question, if I find a blower motor with the same speed, RPM, Voltage and physical size, can I put the 1/2HP motor in my furnace?
Any helpful insight would be appreciated. I'm not looking for step-by-step directions. I'm an electrical engineer and more than capable of changing out the motor. I just don't know all the specifics of an HVAC system, specifically the furnace and don't want to waste time and money pursuing something that really isn't plausible.
Here are some system details to help with any advice:
A/C Condenser: Trane XR Model 4TTR4042L1000AA
Furnace: Lennox Model ML180UH090P36B-03
Blower Motor: Lennox PT No. 100649-01 115V 1/3HP 4SPD FLA 4.87A 1075RPM
Potential Motor Replacement: 5840 PSC Furnace Blower Motor, 1/2HP, 4SPD, 115V, 1075RPM
Since the new condenser and coil installation, I've had a difficult time cooling the house in the summer. Recently, I've been having even greater issues. The blower motor will kick on and off over and over again for seemingly 5-10 minutes before kicking on and blowing air through the duct. I initially thought the capacitor might be an issue, tested it and saw that it was testing well below it's rating so I replaced it. No dice, still seeing the same issue. This tends to occur mostly in the late afternoon/early evening time frame after the AC has been running nearly all day.
I'm starting to suspect the blower motor is failing and started looking into replacements. This had me dig into the service manual and I found that the blower motor is a 1/3HP motor rated for 2-3 tons of add-on cooling. I'm assuming that means that the blower motor is good for up to a 3 ton AC unit. My AC unit is 3.5 tons. I'm wondering if this is the reason they system hasn't been able to cool my house as much as I would like and also the reason why the blower motor is failing. Is it possible the the blower motor is working too hard all day to try and move that level of air and then overheating by late afternoon?
So I'm wanting to replace the blower motor and I'm thinking I ought to up-size it. The service manual shows the blower motor size for the next size up furnace from the one I have and it is a 1/2HP rated for 3-4 tons of add-on cooling. My main question, if I find a blower motor with the same speed, RPM, Voltage and physical size, can I put the 1/2HP motor in my furnace?
Any helpful insight would be appreciated. I'm not looking for step-by-step directions. I'm an electrical engineer and more than capable of changing out the motor. I just don't know all the specifics of an HVAC system, specifically the furnace and don't want to waste time and money pursuing something that really isn't plausible.
Here are some system details to help with any advice:
A/C Condenser: Trane XR Model 4TTR4042L1000AA
Furnace: Lennox Model ML180UH090P36B-03
Blower Motor: Lennox PT No. 100649-01 115V 1/3HP 4SPD FLA 4.87A 1075RPM
Potential Motor Replacement: 5840 PSC Furnace Blower Motor, 1/2HP, 4SPD, 115V, 1075RPM