I`ll start off first with what I have,it is a split freezer plate in a box with a txv,then has a small plate box that you sit ice trays in which is in a upper box it has its own txv.The condensing unit is in the bilge.By the way this freezer setup is in a 45 ft sport fishing boat.Any way The original condensing unit was eaten up from corrosion,the service valves were leaking and had several other leaks.So I replaced the 1/4hp condensing unit with similar unit.I charged with nitrogen checked for leaks ,let it out pulled a 15 min vac,broke vac with nitrogen then pulled a 45 min vac below 500microns.I`m using hotshot to charge this,as I `m charging the pressures looked okay,low side around 0 high was nearing 100psi,then the low side started in a vac and high started climbing,first thought was restriction at txv.Sure enough,no flow out of txvs.I blew through it and it was stuck,tapped it a couple of times and it opened.I replaced both txv`s.Did the same procedures as above,then went to charge,the same thing happened.It seems that the liquid is causing the txv`s to stick.You have to charge hotshot in a liquid state.I also used a liquid charge adapter on my cylinder.I`m not sure what is causing this.Moisture?Anybody else have seen this?