I'm having issues with a rtac200 closing the alarm relays #1 and #2 for a "low chilled water temp: unit off" in the colder nights. The temp will typically be around 36 and 38* ENT/leaving when I arrive in the am and will show the alarm which is auto reset. I have changed the alarm options to latching alarms only which has taken care of the problem but there is no way to have a circuit specific latching alarm relay. So I have no way on the front end to know if either circuit is in alarm or both. I do have glycol in the system and pump control set above my freeze point for protection. The configuration in the chiller for evap is "with freeze protection". Also i will get alarm for evap water flow overdue as the chiller wants to control the pump but the bms is and sometimes a low evap temp unit off.