I have a room at a walk in cooler and I have a room at 34 degrees, I always see recommended superheat for pretty much everything at 8-10 but the sporlan pro app suggests 13* superheat.
No real problems with the temps in this room but there is a giant block of hard/clear ice on every evap after the EEV and on the distributors.
The temperature/ lsv for each unit is controlled by a plc and by terrible design if it is .1 above setpoint it turns on and .1 below and it turns off. Which means these units pretty much click on and off every few minutes. I'm thinking ill drop the SH to 10 or lower and that way the evap will drop further below setpoint than it currently does and have a little bigger of an off cycle. If that doesn't work i'll probably have the programmer put in a deadband
I've been curious, when it comes to the superheat which I should go with the 8-10 or 13 and if it even matters and why.
Thanks yall, i really appreciate all the help and information you guys give. :grin2: