Looking at installing this thing in the attic. The Sante Fe website says the Ultra205 can operate in 34-135 F. My HVAC contractor sounds skeptical. Anyone knowledgeable have thoughts one way or the other?

Thanks,
 
I moved your thread to the "AOP Residential HVAC and Refrigeration (Beenthere Zone)" forum as this is the only forum where homeowners can ask non-technical HVAC/Refrigeration questions, and seek advice.

Please take note of this new location as the "Moved" icon in the other forum will only last a day.
 
Save
Discussion starter · #6 ·
Those specs also state the "inlet air temp" must be in the 49Âşf to 95Âşf range.
Yes, the plan was to have the dehumidifier installed in the attic with the supply and returns ducted to the existing HVAC. I'm not in the trade, so forgive me if my understanding incorrect, but was assuming the "inlet air temp" was the air running through the ducts, which should always be in that range.
 
This is for a commercial application.
Post # 1
" ... Looking at installing this thing in the attic. ... "
=================

WHAT Commercial Building has AN ATTIC.??

How large is this Commercial building?
60' X 160' ?
 
Save
Discussion starter · #8 ·
Post # 1
" ... Looking at installing this thing in the attic. ... "
=================

WHAT Commercial Building has AN ATTIC.??

How large is this Commercial building?
60' X 160' ?
It's a 15,000 square foot single-story day care center. It is wood frame with an unconditioned attic. We have 8 rtu's on the roof.
 
Save
Not sure where this is going...
It will eventually get to a defined WORK SCOPE necessary to address required Outside Air requirements.

WHAT are the SIZES of each of the 8 RTU's? _______ ~ 30 to 46 tons total

RTU model #s:

How much Outside Air is currently set-up on each RTU.?

ZIP _ _ _ _ _ ?
 
Save
They should be good numbers. The Unit does not use the attic air for any functions.

Keep us posted on any difficulties.

Regards Teddy Bears
 
Save
They should be good numbers. The Unit does not use the attic air for any functions.

Keep us posted on any difficulties.

Regards Teddy Bears
How effective is one SantaFe Ultra 205 dehumidifier in provided the required dehumidification
and OUTSIDE AIR for a 15,000 Sq Ft DAY CARE CENTER ?

https://codes.iccsafe.org/content/IMC2021P1/chapter-4-ventilation

IMC 403.3.1.1
___ Summary: 10 CFM / person + 0.18 CFM/ Sq Foot

____ = 10 * 25 + 0.12 * 1000 = 250 + 180 = 430 CFM per 1,000 Sq Foot Day Care Area [ < 5 year olds ]

=== === ===

Post # 8

" ... It's a 15,000 Square Foot single-story, Day Care Center.
It is wood frame with an unconditioned attic.
We have 8 RTU's on the roof. ... "
 
Save
I do not feel qualified to comment on the number of units needed to get the unknown effect on the space.

Usually in this type of building, a specific sized dehumidifier is added to each air handler.

It depends on what effect you want on the space. A day care space low-no occupancy evenings. This may reduce the dehumidification needed evenings.

How much fresh air leakage and mechanical ventilation is another issue. Its about these issues that we need more info to comment on number of units. The SFU 205 is a large unit requires more care with location and duct connection to avoid sound issues than a 155H or 120H.

Dan, I agree issue about the question of "how many?" to meet what specs?

More real info on the issues for me to comment. Trying one unit on an area, OK.

Regards Teddy Bear
 
Save
Discussion starter · #15 ·
How effective is one SantaFe Ultra 205 dehumidifier in provided the required dehumidification
and OUTSIDE AIR for a 15,000 Sq Ft DAY CARE CENTER ?

IMC 403.3.1.1
___ Summary: 10 CFM / person + 0.18 CFM/ Sq Foot

____ = 10 * 25 + 0.12 * 1000 = 250 + 180 = 430 CFM per 1,000 Sq Foot Day Care Area [ < 5 year olds ]

=== === ===

Post # 8

" ... It's a 15,000 Square Foot single-story, Day Care Center.
It is wood frame with an unconditioned attic.
We have 8 RTU's on the roof. ... "
We are looking at installing multiple dehumidifiers, not just one. I didn't provide all details in my original post to keep is brief and concise. Here's the background on why we are even looking at this if your are interested:

Building was built in two phases -- Phase 1, 10K square feet was finished in 2019, Phase 2, 5k square feet was finished in 2022. We are in Zone 4. We have been having excessive humidity in the building every July-Sept.

2019 - We brought it to the GC and HVAC installers attention, HVAC installer said the building just needed to dry out and it would not be an issue after that.
2020 - We wait a year, the next summer it is still super humid (consistently mid 60's into 70's, sometimes into 80s). GC and HVAC installer troubleshoot the system, try a few different things like adjusting OA and fan speed, but it doesn't noticeably change. Phase 2 was already in the planning stage and the mechanical engineer (different from HVAC installer) recommended we install RTU's with gas re-heat in the Phase 2 area, saying that would address the humidity.
2021 - Phase 2 is completed in late 2021
2022 - Summer comes and humidity is still an issue, despite adding the re-heat RTUs. We have third party HVAC designer come in and inspect the system. They recommended a TAB done since none was ever done for the system. TAB was completed in late 2022.
2023 - Summer comes and humidity is, again, still and issue. GC has engineer come out to look at everything, he says everything is working as designed and he has no explanation for humidity. HVAC contractor tries a few more tweaks.
2024 - Summer comes and still humid. GC has a third party engineer look over the plans to get opinion on system sizing, according to GC, thir-party engineer says it looks reasonable. GC and HVAC installer propose installing dehumidification system, but stated that they do not think the HVAC system is the source of the humidity and that it has to be coming from some other source. HVAC contractor wants to install a single Quest 876 in our resource room. My concnerns with this are:

1) This will take up significant space in that room
2) Very expensive, given it's not addressing the cause of the humidity, just the symptom of the issue
3) I'm not convinced a single unit in that room will adequately serve the whole building from that location. (Dehumidfier will have an open return side and the supply will be ducted to the 4 rtu's in Phase 1.)

Given the above, I asked about installing multiple units like the Santa Fe unit in the attic, but the HVAC contractor said that would be significantly more expensive and was skeptical that they would work properly if installed in the attic. We do not have excess space to put these units inside the building.

So that's where I am today.

Notes / Specs

Phase 1

RTU 1 - Trane YSC092 - 7.5 Ton | 2800 CFM | 700 OA
RTU 2 - Trane YSC092 - 7.5 Ton | 2700 CFM | 750 OA
RTU 3 - Trane YSC092 - 7.5 Ton | 2700 CFM | 750 OA
RTU 4 - Trane YSC102 - 8.5 Ton | 3100 CFM | 800 OA
MUA 1 - CaptiveAire - 1600 CFM (kitchen)
Commercial kitchen hood - specs unknown
Exhuast fan for bathrooms

Phase 2

RTU 5 - Lennox KGB048S - 4 Ton | 1500 CFM | 500 OA (min?)
RTU 6 - Lennox KGB036S - 3 Ton | 1100 CFM | 250 OA (min?)
RTU 7 - Lennox KGB048S - 4 Ton | 1600 CFM | 475 OA (min?)
RTU 8 - Lennox KGB036S - 3 Ton | 1100 CFM | 400 OA (min?)
** I believe these 4 RTU's also have CO sensors to control OA
 
Do you have any records of the actual temp/%RH that are typical? During the hottest days, your a/c should be able to remove significant amounts of moisture that should remove the moisture from the fresh air and occupants to maintain <50%RH. Many do not appreciate the significance of setting air flow of the amount of air flowing through the cooling coil to make the a/c cooling coil cold enough to cool the air has a supply dew point that is 5-7^F below the desired dew point in the space. An example would be, you want 75^F, 50%RH, a 55^F dew point, your a/c must supply <49^F dew point air. This about 3 lbs. of moisture per ton per hour of dehumidification. This will maintain 50%RH, a 55 dew point. If you are bring in excess fresh air or the units have access air flow, an adjustment is required.

In summary, During peak summer heat, a properly sized and setup a/c should be maintain <50%RH. As the sun sets, the sensible cooling load declines less moisture is removed and thats when the dehumidifiers or reheat is required. The same applies to rainy days or days of +60^F outdoor dew point.

You follow this so far?

Regards Teddy Bear
 
Save
Save
It's a 15,000 square foot single-story day care center. It is wood frame with an unconditioned attic. We have 8 rtu's on the roof.
Depending on your location there are specific requirements for places of public assembly.
You need an engineering firm.
 
Depending on your location there are specific requirements for places of public assembly.
You need an engineering firm.