recharging a dehumidifier?

15K views 15 replies 5 participants last post by  R600a  
#1 ·
I know this is a crazy idea, but I found one in good shape on the side of the road. Super low on charge, compressor runs until it gets hot then shuts off and just the slightest bit of condensation forming on the cap tube.

I miraculously did find the leak, a pinhole right by where the drier is brazed in.

For charging this thing, (R410) I was just going to charge it until it hit say 10 deg SH, but is there any sort of spec I should be looking for, or would it just be better to try and find the factory charge weight and weigh it in.
 
#2 ·
Usually the factory charges listed on the sticker If the sticker is still present. Personally I don't bother weighing it in when I recharge my leaky dehumidifier I added a little bit of leak stop and I charged it up by superheat while watching discharge temperatures and monitoring it for quite a while of runtime I don't remember the exact numbers but I got it working pretty good.
 
Save
#3 ·
Save
#4 ·
The by-feel charge wants to be: no frost on the evaporator coil and a cool suction line at the compressor - but not beyond that. If the side of the compressor below the suction line connection is also cool - the system is overcharged.

PHM
-------
 
Save
#9 ·
Still; just changing & monitoring establishes a baseline. Does the refrigerant leak out in a month or in two years?

What is Your Goal? Is the primary goal to have a dehumidifier this summer? Or is the primary goal 'to do it because you want to do it'? <g>

PHM
-------
 
Save
#8 ·
If you have the spare time, pull the gas, braze the leak (you already found it, half the battle is over), pump it down and weigh it in. Note the numbers with the factory charge in Sharpie on the back panel, then if it leaks again, you know exactly where to top it off to. It'll only take a couple hours, you know it's not contaminated since the leak's on the high side, so you can probably skip replacing the drier and a long pump down.


Sent from my Pixel 6 using Tapatalk
 
#11 ·
Brand name?

Teddy Bear
 
Save
#13 · (Edited)
I decided that the piercing valve will probably leak worse than the pinhole and it’s not worth the effort of fixing it beyond getting it running. Gave it my old standby by feel charge of once all the evaporator coils are cold and sweating, and the suction line immediately after is just starting to sweat (automotive I always did so the inlet and outlet felt about the same on orifice tube systems), and called it good enough. It’s doing what it needs to do!
 