Receiver goes back into cond coil ?

14K views 61 replies 19 participants last post by  UmmScott  
#1 ·
New Kolpak walkin Freezer 448a

1 - Why do you suppose they route the liquid lines that way ??

2- This is outdoor condenser , why didnt they use a headmaster ? They BRAZED in a cheap fan control which broke 2 years later ...which is why I was there. i installed a Ranco fan control.
 

Attachments

Save
#5 ·
That P66 is a little pricey ..

The fan motor didnt even say where it was made

Part number on fan is 11623E

Im not sure if that motor would like a variable speed ... but then again Im not sure which is worse , variable , or turning on and off a bunch
 
Save
#13 ·
Ha ... you cant see it apparently

The suction insulation is so massive , like 4 inches wide , that it hides it below , its mounted under that suction pipe
 
Save
#21 ·
A receiver sucks away most of the subcooling. You can't get it back by simply using a larger condenser or by adding more refrigerant, like you can with systems that don't have a receiver. There are 2 ways to increase subcooling. One way is with the condenser subcooling loop like we have in this example, the other way is with a heat exchanger between the suction line and liquid line. The heat exchanger method seems to be most popular, especially on small cap-tube coolers where the cap tube and suction line are often soldered together. The problem is that this raises superheat, which usually isn't a good thing.

While I'm here I'll point out that I think PHM made a little typo on his advice. He's got 2 cut-in settings, and no cut-out, LOL. His advice is very good though. I think most people who set up fan cycling pressure switches try to set them up with too narrow of a band. His advice is to make it as wide as possible. He's also saying that most expansion valves are designed to work with a minimum 100psi differential between their inlet and outlet. I don't think a lot of people know this about expansion valves. So anyways, you use the normal suction pressure plus 100 psi to figure out where to set the fan cut-out, and about 130° (converted to pressure) to figure out where the cut-in should be.
 
Save
#24 ·
I'm not so sure about that minimum of 100psi PD across the TXV, @ a 40*F Evap Temp. The point of 100psi PD across a R22 TXV is the "rating point" of the TXV. Such as a r22 1 ton TXV is actually .93T @ a 100psi PD across the TXV. And that same TXV is rated as a .73T txv at a minimum shown press drop of 60psi, as shown in the "Extended Capacity Tables". And the max PD is 175psi (1.23T)PD for that same TXV, again in the Extended Capacity Tables. I think.
 
#39 ·
There was a discharge superheat thread somewhere that was really good too.

Sent from the Okie state usin Tapatalk
 
Save
#51 ·
Interesting. Thanks for posting that icy78. But why would we care if refrigerant migrates from the "warm receiver to the cold condenser" during the off cycle? I suppose it's so you don't have a few seconds with a flashing sight glass upon startup again? Doesn't seem like a big deal to me. Am I missing anything?

I'm guessing the scroll compressor has a check valve built into it as well, correct?
 
Save
#54 ·
I may be wrong here but here's what I think they are trying to accomplish.

We often install outdoor units with heated and insulated recievers around here for extreme cold conditions. Its necessary to keep receiver pressures high enough to come out of pumpdown after long off periods when it's -20F or colder outside. A unit with an HPR or "headmaster" acts as a quasi-check valve since it closes to the condenser when the receiver pressure drops, thus helping prevent (but not necessarily eliminating) migration back into the condenser which would happen readily when its cold outside since the condenser is obviously designed for heat rejection. Since this unit has only fan cycling they may have added it to discourage migration and low head pressure when it comes out of pumpdown. I have seen several of these units however that work just fine in pretty cold weather without the check valve. I think it also serves the purpose of preventing flashing due to the fan cycling as mentioned too.
 