Ok, long story.
Tech shows up, customer says place was remodeled last year, unit "worked fine last year, after remodel".
Straight cooling Air handler/AC.
Tech finds 120 to unit.
Finds 13v on low voltage.
Changes transformer wiring to 120. Motor spins slow, flips breaker off.
Calls me, wants to know if he can change the motor to a 120 motor.
Tell him: "absolutely not. You've modified that unit's UL. tell them it needs to be 220. You can charge them to fix it if you want, just make sure it's a homerun."
Calls me back:
"'**** dude, ****. The motor threw sparks when I changed it. The guy is on his way home from work, and doesn't want me to touch anything electrical, because he wired the whole house.'
'fine, put the electric back. That motor is smoked. I don't care what he says, he broke it.'
guy gets home. Tech tell him he smoked motor, doesn't believe him. Switches wiring real quick at panel, motor throws sparks and runs. Says "see, it's fine."
Anyways, what a cluster.
Here's another one.
Lets say I had a 220 fan motor that I needed to spin the opposite direction, and didn't have the yellow/orange leads you can switch, lets say it's a stock motor.
brown = cap, black = L1, blue = cap common (L2)
If I switch brown/blue, on the capacitor, the fan will run backwards.
Checked my amp draw, looks good.
Will it kill the motor?