How long before you can use the nat gas. If its 4 or more years. Well, LP is real expensive.

Other then that, it doesn't make sense to get a mod/con boiler if the gas is free.
Especially with all the filter and drier system you will have to install. That gas won't be clean of dry.
 
You might want to run your pumps lil longer then your boilers on shut down to get the extra btu's...out or your water...
If the boilers on an OD reset, they isn't going to be much in the way of extra BTUs.
If the circs run too long on a nat draft boiler, you can pull heat from your mass back to teh boiler.
 