Why would the inlet pressure be reduced ?
If that was the case every walk-in cooler / freezer with multiple evaporators on the same liquid line would have capacity issues.
 
Ehsx seems to be saying he doesn't think that's the case.

Personally, I believe that's what the crimp is - an orifice.

Sent from my E7110 using Tapatalk
We don't know the I.D. of what appears to be a 3/16" line also they added a loop I'll assume to acquire a certain length.
That said, the line itself could be the metering device.
 
Hi all,
Thank you very much for your replies.
Yeah, I'm from Asia country, so time zone might differ.
I've got the answer:
That bypass captube is to provide more capacity. Why not using higher capacity TXV: Lower capacity TXV provides more precise control. Those short capacity would be compensated with the bypass captube.
I'll revert back to the OP ☝🏻
 