Is anyone else having trouble pulling vacuums on Mitsubishi mini-split systems with multiple indoor units? It pulls very slowly and doesn't hold. This has happened on multiple occasions. I can pull the vacuum for 90 minutes, breaking it with nitrogen twice, and still only reach 800 microns. As soon as I valve the lines off the microns jump up. I've ruled out leaks in the systems and my equipment. I'm thinking moisture is trapped inside and is very difficult to remove since the system only has a service valve on the suction line. I've tried pulling the vacuum quickly and slowly.

This has been very frustrating.
 
#5 ·
Like I said, I've ruled out my equipment. I pull down every other system I work on without trouble, regularly going below and holding 200. I have also tried 2 different equipment setups, both work on every other system I've done.

Unfortunately, I don't have the luxury of pulling a longer vacuum since I don't get to these jobs until late afternoon. I'm hoping someone out there knows a trick to this. I wish these things had a liquid line service valve!
 
#6 ·
Multiple access ports, multiple pumps and time are your friend. 90 minutes isn't enough. I've pulled on multis over 8 hours before to get down to a good level. Just a ton of volume to evacuate.
Might want to check your recommended pressure test psi. All my equipment is between 500-600 psi for minimum 24 hours.
Are these conventional style outdoor units with only one access port? What size pump are you running?
 
Save
#9 ·
The systems only have one access port. I'm using an Appion TEZ 8 with a 1/2" hose and core remover. Also tried using my SMAN3 manifold. No uncapped service ports. It sounds like there's no quick fix for this, and that the process needs more time than I'm alotted.
 
#10 ·
More time my friend. Evacuation isn't something you can hurry along.
I did a Samsung today with 3 indoor fan coils. Been holding 600 psi for close to a week so no leaks. Took around 4.5 hours to get the micron gauge down where I wanted it, holding of course. Thats pulling with an 8 CFM pump, both lines (it had service valves), cores removed.
 