We replaced a 3 hp rooftop condensing unit for a medium temp walkin refrigerator.
It worked all winter, this summer we had a problem with the box being warm 45° I replaced the expansion valve with a 3 ton valve, it only had a 1.5 ton valve in it and we had very high superheat. The temp dropped down to 35°
But I had to add 20# r22 to get the sight glass to clear up , we didnt recover any gas I pumped it into the reciever ,presure tested and vaccumed the line before opening. The first day it went to 90° outside I had to recover about 5#to keep the unit from going off on high head.
Here is my question I trying to figure out wether its the OROA head pressure control or do i have a reciever with no dip tube to the bottom or am I missing something. There is no trouble shooting guide for the OROA.
Thanks
Rich Traupmann
It worked all winter, this summer we had a problem with the box being warm 45° I replaced the expansion valve with a 3 ton valve, it only had a 1.5 ton valve in it and we had very high superheat. The temp dropped down to 35°
But I had to add 20# r22 to get the sight glass to clear up , we didnt recover any gas I pumped it into the reciever ,presure tested and vaccumed the line before opening. The first day it went to 90° outside I had to recover about 5#to keep the unit from going off on high head.
Here is my question I trying to figure out wether its the OROA head pressure control or do i have a reciever with no dip tube to the bottom or am I missing something. There is no trouble shooting guide for the OROA.
Thanks
Rich Traupmann