Here's my situation. At my work I have a 20,000 square foot office building, 10,000 sq. feet each floor. Top floor cooled by 40 ton Carrier split system, bottom floor by 20 ton. Air handlers on both floors are variable frequency drive feeding on average six or seven VAV boxes per floor.
Air handler VFD is controlled by a VTAC 7 HVAC Drive. Variability in fan speed is determined by remote static pressure sensor in ductwork at (what I'm told) most remote location in trunk. Here's the deal:
Top floor, VFD will vary with load throughout day. More VAV boxes open up, VFD compensates by increasing motor speed to move more air. VAV boxes ramp down, so does VFD. VTAC 7 Drive readout set to indicate hertz of motor at various speeds, varies from 49 to 54 HZ recently.
Bottom floor, VFD runs dead solid one speed. Regardless of how many VAV boxes open up or ramp down. The display on VTAC 7 displays a solid 52.5 HZ.
So, being that I'm on the learning curve with this system, and being that I had to be here at my building today on my day off to supervise roof repairs, I wanted to find out why the bottom floor variable frequency drive never varies. I first checked out the top floor, hooking my meter to the sensor leads from the static sensor to see what kind of variability it feeds back to a small controller outside the VTAC 7 (all it says is UCM-420A on the small controller). It read 27.xx volts, the "xx" is what varied as I went around the building setting VAV boxes colder, then warmer. I repeated this test downstairs, and also noticed "xx" variability as I adjusted the VAV load throughout the building (building empty today...lets me play with stats without freezing anybody out).
That tells me both static sensors appear to be returning valid input to the controller, unless I'm using the wrong method to test for such. That's one thing I need to know. The other being that if everything external to the drive is giving input, but bottom floor drive seems unresponsive, is that an internal matter with the drive, such as an incorrect parameter in the setup programming?
And finally, the lack of variability doesn't seem to affect the building's cooling performance all that much, but I wonder from a static pressure point of view if there's concern. During low load conditions, the VAV's will close but the VFD doesn't slow. I recently lowered the fan speed manually as I was losing gearboxes on the Enviro Tech VAV boxes, which seems to tell me static was too high.
Also, being that my employer paid for a frequency drive system, the damn thing should vary!
I'd appreciate any info you guys may have. I haven't touched anything regarding the drive's programming, although I do have the book. I'm not willing to jump in and do anything wildass; I want to know what's involved beforehand.
Thanks in advance.
Air handler VFD is controlled by a VTAC 7 HVAC Drive. Variability in fan speed is determined by remote static pressure sensor in ductwork at (what I'm told) most remote location in trunk. Here's the deal:
Top floor, VFD will vary with load throughout day. More VAV boxes open up, VFD compensates by increasing motor speed to move more air. VAV boxes ramp down, so does VFD. VTAC 7 Drive readout set to indicate hertz of motor at various speeds, varies from 49 to 54 HZ recently.
Bottom floor, VFD runs dead solid one speed. Regardless of how many VAV boxes open up or ramp down. The display on VTAC 7 displays a solid 52.5 HZ.
So, being that I'm on the learning curve with this system, and being that I had to be here at my building today on my day off to supervise roof repairs, I wanted to find out why the bottom floor variable frequency drive never varies. I first checked out the top floor, hooking my meter to the sensor leads from the static sensor to see what kind of variability it feeds back to a small controller outside the VTAC 7 (all it says is UCM-420A on the small controller). It read 27.xx volts, the "xx" is what varied as I went around the building setting VAV boxes colder, then warmer. I repeated this test downstairs, and also noticed "xx" variability as I adjusted the VAV load throughout the building (building empty today...lets me play with stats without freezing anybody out).
That tells me both static sensors appear to be returning valid input to the controller, unless I'm using the wrong method to test for such. That's one thing I need to know. The other being that if everything external to the drive is giving input, but bottom floor drive seems unresponsive, is that an internal matter with the drive, such as an incorrect parameter in the setup programming?
And finally, the lack of variability doesn't seem to affect the building's cooling performance all that much, but I wonder from a static pressure point of view if there's concern. During low load conditions, the VAV's will close but the VFD doesn't slow. I recently lowered the fan speed manually as I was losing gearboxes on the Enviro Tech VAV boxes, which seems to tell me static was too high.
Also, being that my employer paid for a frequency drive system, the damn thing should vary!
I'd appreciate any info you guys may have. I haven't touched anything regarding the drive's programming, although I do have the book. I'm not willing to jump in and do anything wildass; I want to know what's involved beforehand.
Thanks in advance.