18 years ago, one of the big wrenches called me outta bed, telling me to bring as much r-22 as i can get and get to the site to help him asap. was a server room with a 15t air cooled liebert system 3. found out he's been there all nite, with 3 mt jugs strewn about. he was excited as i entered, looking behind me for more freon.checked his work, circuit dropping out on l.p., as such, he kept dumping in more gas. 'did you check the l.l. solenoid?' 'what solenoid?' checked and found it wasn't energized. i opened the disconnect, reset it, and the unit took off momentarily until it quit on hp. had to remove all the juice previously installed
 