I would appreciate some expert advice on problems I am having with my Riello 40 Burner.
Background: In 2009 I had an HVAC contractor install a Biasi B10 boiler with a Riello 40 burner. This system replaced an aging Dunkirk Blue Circle boiler with a Blue Angel burner. With the original system, two oil pipes were connected and run to the top of the oil tank in the garage (Approx 25-30 feet away). With the new Biasi/Riello installation, only one of the oil pipes was connected to the burner oil pump; the other oil pipe is laying on the boiler room floor (and I assume it is capped).
This new system has worked without issue for 4 years. The pump was pulling the oil up out of the top of the tank without issue.
In November of 2013, I had my oil company service the burner. I was at work at the time, but was hearing that the guy was having problems; he was at my house about 4-5 hours.. ultimately I was told that with the cleaning he had broken the suction, and the oil had returned to the tank.. the pump was unable to self-prime. The resolution at the time was to use a push-pull pump to draw the oil from the tank to the burner. Everything was up and running.
In the interim, I had spoken with the head Boiler guy at the oil company, and we discussed the matter of Riello pumps requiring a gravity feed from the oil tank. He told me that we shouldn't have an issue going forward, and that he would just keep it noted that at future cleanings, techs should break out the push-pull pump if the pump loses the priming. I had asked whether connecting the second oil pipe to the pump would eliminate this problem.. I didn't get a definitive answer as to whether this was necessary or recommended.
This morning, I awoke to no heat. I called the oil company, and, of course, the tech had to use the push pull pump to reprime the Riello pump, and $ later, we are up and running, albeit I am rather sore about the bill.
My questions to you:
1) Is a 1-pipe system pulling from the top of the oil tank an incorrect installation? Note that the oil is pulled up out of the tank, but then drops down to floor level at the boiler. The basement is now finished so it would be disastrous to consider changing anything about the piping run.
2) Can, and should, the second pipe be connected to the Riello pump for a 2-pipe system? The second pipe is already laying there, and so I imagine this could be done with 1-2 hours labor. Is this the proper way to have installed this system, and could you tell me if, in your opinion, this will definitely eliminate any issues with the priming of the oil pump?
Thank you so much for your time and consideration. As you might imagine, I am already kind of peeved that I am throwing money at a young 4-year-old installation which I wouldn't have expected any issues from. I appreciate your expert advice.
Craig
Background: In 2009 I had an HVAC contractor install a Biasi B10 boiler with a Riello 40 burner. This system replaced an aging Dunkirk Blue Circle boiler with a Blue Angel burner. With the original system, two oil pipes were connected and run to the top of the oil tank in the garage (Approx 25-30 feet away). With the new Biasi/Riello installation, only one of the oil pipes was connected to the burner oil pump; the other oil pipe is laying on the boiler room floor (and I assume it is capped).
This new system has worked without issue for 4 years. The pump was pulling the oil up out of the top of the tank without issue.
In November of 2013, I had my oil company service the burner. I was at work at the time, but was hearing that the guy was having problems; he was at my house about 4-5 hours.. ultimately I was told that with the cleaning he had broken the suction, and the oil had returned to the tank.. the pump was unable to self-prime. The resolution at the time was to use a push-pull pump to draw the oil from the tank to the burner. Everything was up and running.
In the interim, I had spoken with the head Boiler guy at the oil company, and we discussed the matter of Riello pumps requiring a gravity feed from the oil tank. He told me that we shouldn't have an issue going forward, and that he would just keep it noted that at future cleanings, techs should break out the push-pull pump if the pump loses the priming. I had asked whether connecting the second oil pipe to the pump would eliminate this problem.. I didn't get a definitive answer as to whether this was necessary or recommended.
This morning, I awoke to no heat. I called the oil company, and, of course, the tech had to use the push pull pump to reprime the Riello pump, and $ later, we are up and running, albeit I am rather sore about the bill.
My questions to you:
1) Is a 1-pipe system pulling from the top of the oil tank an incorrect installation? Note that the oil is pulled up out of the tank, but then drops down to floor level at the boiler. The basement is now finished so it would be disastrous to consider changing anything about the piping run.
2) Can, and should, the second pipe be connected to the Riello pump for a 2-pipe system? The second pipe is already laying there, and so I imagine this could be done with 1-2 hours labor. Is this the proper way to have installed this system, and could you tell me if, in your opinion, this will definitely eliminate any issues with the priming of the oil pump?
Thank you so much for your time and consideration. As you might imagine, I am already kind of peeved that I am throwing money at a young 4-year-old installation which I wouldn't have expected any issues from. I appreciate your expert advice.
Craig