I recently got back into the field from on-site maintenance I have never seen a multi volt compressor not even in my wholesale days. Second why would you trap a liquid line?
Yes never seen them on liquid not sure of the thoughts of the person installing it.I’ve seen traps on discharge lines. From the pic I’m assuming that’s the liquid line though?
The trap is for oil, not condensed liquid.So the discharge gas could condense on the way up dropping liquid down to the trap ?
How did you know it was a discharge line was it the only thing that made sense ?
The trapped line is a discharge line so the trap makes sense.
The insulated line must be subcooled liquid, hence the need for insulation.
My guess is the discharge line goes to an air-cooled condenser, then to a receiver and then back to the condenser for subcooling.
A couple of med temp evaps hanging in a large walk-inCrazzy what's up on the roof ?
Unfortunately no it’s a liquid line in a med temp wiThe trapped line is a discharge line so the trap makes sense.
The insulated line must be subcooled liquid, hence the need for insulation.
My guess is the discharge line goes to an air-cooled condenser, then to a receiver and then back to the condenser for subcooling.