What is the minimum acceptable voltage on a 208/230v 1ph condenser? Customer has a unit with a static 206v and the compressor is unable to start if there is any residual head pressure on the system causing some breaker trips on hot days.
This of course is just my opinion, I would say, anything below 208 is not good, and I personally believe the mfg. would agree.Compressor says 208-230 1PH.
Voltage drops as low as 198 on start up.
My question is would we call 208 +/- 10% good? Or is 208 the MINIMUM voltage?
Not disagreeing with you here, but is there some documentation from the compressor/compressors mfg. that says this?But required voltage plus or minus 10% is the accepted rule.
I understand, and I’m not even from Missouri “show me state” but can you provide some documentation or even a link to something that says that from the manufactures."...motors are sold and warranted for voltages no lower than 10% under the value on the motor nameplate. This is a NEMA requirement."
I’m a Ruud dealer, so I should be able to find this information pretty easy.Cant post pictures but the installation manual for a Rheem RA13 states that the minimum/maximum voltage for a 208/230 1phase system is 187-253 which is +/- 10%.