I'm having a problem with the background download.
Let me explain,
When I run the automatic reset from SCTPro to change the SNE version, the download stops progressing at a certain percentage (63%).

Error message: Object reference not defined to an instance of an object

Although:
  • I changed the network type to private network
  • I added the two rules in the firewall: "Metasys (TCP Protocol)" and "Metasys (UDP Protocol)"
  • I disabled all unnecessary network cards to minimize communication errors between the SCT server and the SNE
  • I launched and kept the NAE Update Tool application open before and during the SCT download

None of these tips worked

Have you ever had a similar problem?
Can you help me?

@PID loop
@NickDeal
Thank you
Is your network profile switching back to public when the device reboots mid-flash? I've had this problem when trying to flash black engines on a direct ethernet connection. If you use a 5-port dumb switch, your connection will not refresh when the SNx reboots, thus maintaining the private property.
 