Have a Trane XV80 in the attic. Also in the attic laying next to air handler is a Relay Panel (Trane BAY24VRPAC52DCA). In the hallway is the Trane thermostat (model# TCONT850AC52UBA)
Noticed A/C wasn't working last night. Thermostat display is blank (appears un-powered). Checked drain pan water sensor and additional float sensor on the condensation drain pipe. Both dry.
Opened air handler and after bypassing the panel safety switch, I see the Status LED on main board showing a singe green blink (which per the diagnostic codes listed on schematic attached to unit, means "Standby Mode of Call for Cooling".
Pulled thermostat off the wall and measured 15Vac at red/blue wires. Went into attic and found the same red/blue wires from thermostat connecting to the Relay Panel connections R (hot) and B (Com). Also connected to the R and B terminals are wires that go to main board inside the air handler. (The R terminal wire actually goes thru a float switch on the way to the main board and float switch tests OK)
If I disconnect the R and B wires from the main board at the Relay Panel, the voltage on those 2 wires is 28Vac. When I connect them to the Relay Panel, voltage drops to ~15Vac. It appears the Relay Panel is pulling the 28Vac down to ~15Vac OR the main panel can't produce enough current and voltage is dropping. None of the LEDs on the Relay Panel are illuminated.
(With everything hooked-up, the 15Vac I saw was the first measurement at red/blue wires at thermostat. Subsequent measurements have been anywhere from 7Vac up to 12Vac.)
It appears to me the Relay Panel is bad but would like to find a way to confirm that. Thought of installing a precision resistor in series with the red wire and measure V/D across it to calculate if current is excessive, but don't know how much current it's supposed to draw.
Any ideas to verify if Relay Panel is bad or not??
Noticed A/C wasn't working last night. Thermostat display is blank (appears un-powered). Checked drain pan water sensor and additional float sensor on the condensation drain pipe. Both dry.
Opened air handler and after bypassing the panel safety switch, I see the Status LED on main board showing a singe green blink (which per the diagnostic codes listed on schematic attached to unit, means "Standby Mode of Call for Cooling".
Pulled thermostat off the wall and measured 15Vac at red/blue wires. Went into attic and found the same red/blue wires from thermostat connecting to the Relay Panel connections R (hot) and B (Com). Also connected to the R and B terminals are wires that go to main board inside the air handler. (The R terminal wire actually goes thru a float switch on the way to the main board and float switch tests OK)
If I disconnect the R and B wires from the main board at the Relay Panel, the voltage on those 2 wires is 28Vac. When I connect them to the Relay Panel, voltage drops to ~15Vac. It appears the Relay Panel is pulling the 28Vac down to ~15Vac OR the main panel can't produce enough current and voltage is dropping. None of the LEDs on the Relay Panel are illuminated.
(With everything hooked-up, the 15Vac I saw was the first measurement at red/blue wires at thermostat. Subsequent measurements have been anywhere from 7Vac up to 12Vac.)
It appears to me the Relay Panel is bad but would like to find a way to confirm that. Thought of installing a precision resistor in series with the red wire and measure V/D across it to calculate if current is excessive, but don't know how much current it's supposed to draw.
Any ideas to verify if Relay Panel is bad or not??