Hi all (yall)
I was doing a PM for a customer and when taking the refrigerant readings, I have come to a complete brain fart as to why the system was doing this.
Readings:
Indoor temp: 70 F
Outdoor temp: 68 F
Suction Pressure: 65 PSIG (roughly 10 degrees)
Discharge Pressure: 205 PSIG (roughly 72 degrees)
Suction temp: 61 F
Discharge temp: 64
Superheat: 51 F
Subcool: 8 F
Trane R410A system has a design subcool of 10 +/- 3 degrees so my subcooling is within the threshold.
I did not see a filter drier on either the suction or discharge lines to take a temperature drop across to see if there is more than a 2 degree difference aka change that out. I was going to say something along the lines of a restriction after the TXV within the cap tubes that is starving the evap coil giving me a low suction/very high superheat.
Since my job at this moment is to keep a unit running and make sure that happens through the most basic of ways (contactor changes, new dual run cap or start, etc) I have to call into dispatch and turn the PM into a service call.
So, with that said, anyone want to give their 2 cents as to what the problem might be? I want to know just in case I come across this again.
Thanks,
Michael
I was doing a PM for a customer and when taking the refrigerant readings, I have come to a complete brain fart as to why the system was doing this.
Readings:
Indoor temp: 70 F
Outdoor temp: 68 F
Suction Pressure: 65 PSIG (roughly 10 degrees)
Discharge Pressure: 205 PSIG (roughly 72 degrees)
Suction temp: 61 F
Discharge temp: 64
Superheat: 51 F
Subcool: 8 F
Trane R410A system has a design subcool of 10 +/- 3 degrees so my subcooling is within the threshold.
I did not see a filter drier on either the suction or discharge lines to take a temperature drop across to see if there is more than a 2 degree difference aka change that out. I was going to say something along the lines of a restriction after the TXV within the cap tubes that is starving the evap coil giving me a low suction/very high superheat.
Since my job at this moment is to keep a unit running and make sure that happens through the most basic of ways (contactor changes, new dual run cap or start, etc) I have to call into dispatch and turn the PM into a service call.
So, with that said, anyone want to give their 2 cents as to what the problem might be? I want to know just in case I come across this again.
Thanks,
Michael