What would cause an AC unit to have low superheat and low Subcooling? It was an 80F day and my low pressure was 90 and my head pressure was 263. Now I did added refrigerant but that just made my low pressure go lower and my superheat to go lower. My suction temp was 32 and my evap was 30. System is a 2 ton with a txv and air flow is adjusted for a 2 ton my static pressure is 0.49 across the furnace. I just changed the txv today because it seemed like a txv issue. The new txv helped a little bit but am still having a similar issue. With the new txv installed my low pressure is 105 and my suction temp is up to 52. My head pressure is 310 and my Subcooling is 16 ( I intentionally left it a little overcharged so the unit doesn’t freeze ) but my evaporator also came up to 34F from is previous 30F. My previous temp drop was 13 and the coil was freezing up, today however my temp drop was 17. I’m not sure what is going on, changed the filter dryer as well and also recovered and added new refrigerant. What’s going on?