Low side pressure too low high side pressure too high

33K views 10 replies 9 participants last post by  timebuilder  
#1 ·
Hello everyone, new to the industry and work for a school district so here I am. Pretty much all the equipment I work on is 40yrs old or older. Anyway got a call for a pass through refrigerator not keeping temperature. Temps in the box were @ 75 deg. Compressor was going, hooked up guages and found the pressures all whacked out. Low side was @ 8psi and high side @ 340psi. Compressor was really hot. My first guess was bad tx valve. Don't want to just be a parts changer. R12 system was retrofitted with 401A back in 2002. Just want to be pointed in the right direction. Any help would be greatly appreciated.
Thank You in advanced,
Frank
 
#2 ·
You're on the right track. Get your SH and SC redings and make sure the coil is clean.
 
Save
#4 ·
I agree with 2sac, you probably do need to clean the coil. Your head pressure is WAY too high. With the info you gave it could be a restriction and the unit could be overcharged trying to compensate for the restriction. But once you get your subcool and superheat that will give you a better idea if that could be the problem.
 
#7 ·
You said school whats the room temp ac turned off for the summer, clean the coil, get sh sc and i agree sounds like a restriction, careful on the wiegh in its a conversion from r12 to 401 "mp39" the mfg tag will be wrong

Make sure both coils are clear and fans are running, good luck lets us know
 
#8 ·
ok, finally got around to this unit. I recovered all of the refrigerant and blew out the lines, evap was actually pretty clean. Replaced the drier and pulled a vacuum. Charged the system and all is well. As figured, there was a restriction in the system. Thanks to all for the input:cheers:
 
#11 ·
Our Co has taken on more restaurant refrigeration work in the past month. If there is one commonality to these calls, it is the work of the previous Co.

By cleaning the condensers, recovering the charge, and weighing in to nameplate, we are fixing 90% of the failures.

My boss suggested using the Fume Free Easy Off oven cleaner on the condensers, because they were SO bad. Apparently, there is no maintenance contract, only "repair on failure."


I'm trying to get the boss to order the Ecolab grease stripper.
 