Went out to a call this week on a Trane Hyperion TAM7 Air Handler that I installed a couple years ago. I'll get to the specifics later after the right answer is given on how this code poped up. Ok, we all know there is a saturation sensor and a vapor sensor that calculates superheat for the EEV across the indoor coil. Now lets think of all the reasons that would make a "low superheat" code be on our EEV control board. Let the guessing begin.......its not what you think

The winner gets a high five and thats about it. Cheers

Rock on,
 
#3 ·
With the term 'low superheat' I am gonna assume you mean numerically high... as low charge in a conventional mechanical system.

Short of freon...
Too much airflow...
Non-condensibles...

Just throwing out a few to start the discussion along... :)

Really do not know much about the TAM7's.
 
Save
#4 ·
The code for low superheat means exactly that- numerically low superheat.

With how these units are designed, it's difficult to achieve that code unless the blower fails, the door for the coil is off while running, or possibly sensor reversal.
 
#7 ·
Hmm.

While I don't work on a whole lot of these, I don't think that could happen without defying the laws of physics in some form. :grin:

I don't think the sensors are in a position to allow for that. I could be wrong, though, it's been a few weeks since I've looked at one.
 
#22 ·
Sensors not giving the correct reading. I had that on a TAM8.
 
Save
#23 ·
Stepper motor stuck, check valve stuck open, at indoor unit, blower too slow, dirty filter, r22/r410a dip switch is wrong, sensors bad, coil leaking liquid refrigerant and it's hitting the sensor causing a low reading,


Sent from my iPhone using Tapatalk
 
#25 ·
No one is close yet. I figured someone would have it by now or at least be close.

Low superheat means numerically low # on the "Tam" Trane air handlers. I'm saying its not what you think to try to get you to think. If it was obvious I would have never started this thread.

Think of EVERY possibility that would make that air handler "think" it had low superheat.
 
#43 ·
BAM! You the man bro!

Was doing a PM and pulled the disconnect for the condenser for cleaning and went down to check my air handler and was given this code because there was still a call for cool and air handler was running. No temp drop across coil so the coil was room temp. Thus no superheat. Glad someone was thinking. A lesson for all.

I'm excited you got it. Lunch is on me if you are ever in the upstate of SC. And a high five to go along with it. Congrats Cleter!!!
 
#40 ·
The thermostat is set below 70* and the return air temp is that low.
 
Save