I only got about 1/3 the way through your post until couldn't take anymore. The way you are describing things it seems clear that either you're straight up messing with us, or you don't know the difference between your suction and liquid lines or which direction the refrigerant is supposed be flowing.

The suction pressure can't be 400psi with a liquid line pressure of 65psi. Coupled with this information, I find it hard to believe that the filter drier was actually backwards inside of the condensing unit as you say it was.

Just for my own curiosity, if your pipes are 3/4" and 3/8", which one is the liquid line and which is the suction? Also, which way do you believe the arrow on the drier should be pointing (towards the house or away from the house)?
 
Save
Sorry that I got so long winded. I need to simplify in general. I wonder if there’s a plugged screen hiding somewhere within that condenser unit.

It’s been 25 years since I got out of refrigeration school. My terminology needs some brushing up.
I’ll be perhaps the first to admit that I barely know the difference between my ass and a whole in the ground. But I’m trying to learn.

You ask if I understand basic refrigeration principles:
Cold liquid leaves the compressor and follows the fat liquid line towards the indoor evaporator coil.
Liquid refrigerant can flash to a wet and cold vapor at the piston and then saturate the majority of the evap coil or if it’s a txv system then the liquid refrigerant enters the evap coil and the refrigerant is metered on the outlet by the txv.
Regardless of which metering device is used, the liquid refrigerant boils by the end of the evaporator and then the hot vapor travels via the suction line back out to the condenser unit again to then pass through the filter drier, service valve, condenser coil and lastly the compressor to then restart the whole process all over again.

I wanted to type less verbal descriptions and post a few photos up from the job site but I couldn’t figure out how to post photos.
Interesting. Sorry I doubted you. I'll bet you've found and corrected a lot of backwards filter driers over the years! I don't know what's going on with your unit, but good luck! :munching:
 
Save
I’m sorry that I’ve turned anyone off by incorrectly describing the refrigeration cycle.

Can I briefly bypass the lineset and indoor coil with a different coil and metering device outside at the outdoor unit?

Can I bypass the lineset and indoor coil with a 3/4” x 3/8” coupling? I’d perform a triple evac and charge with nitrogen only to about 300 psi. For a brief test, would that cause any harm?
If you are asking if you can install a temporary air handler with a metering device and evaporator coil outside right next to your condensing unit, I say sure, why not?

If you are asking if you can just take the 2 lines coming out of your condensing unit and hook them together, then NO. That's not going to work very well.
 