I have an outdoor air to air heat pump connected to my forced air furnace.
The backup heat system is electric too: two electric heating elements. One or more of the elements get toggled on when it gets too cold for the heat pump to maintain the internal house temp.
I have noticed recently that when the backup heat is on, the heat pump compressor is still running, even when it is super cold out (like 0°F). Is that normal?
I want to add a level 2 electric vehicle charger to my home, but the electrician says that I can't because it would just nudge the "calculated load" of my electrical service connection over the electrical code limit. Having said that, he then said that if the HVAC control system was such that it only turned on either the heat pump OR the backup heat (but never both at the same time) then my service connection would be enough.
He said it was rule 8-106 Subrule 2/3 in Canadian Electrical Code:
The control system is a Honeywell THX9421 Prestige IAQ with EIM
Looking at the manual for the control system, it says on page 100 that there are backup heat types that allow you more fine-grained control over how backup heating works.
For example, it looks like instead of selecting "electric forced air" as the backup type, the installer could have selected "other" as the backup type and then selected whether or not the backup heat was allowed to run with the heat pump (custom configuration).
Sounds like I might just need to "educate" the HVAC contractor about this possibility and get him to come and re-program my thermostat? Does that sound right? And then my electrician can change his load calculation and save me the 3 kW of the heat pump?
Is there a reason why it would be bad to not run both heat pump and backup electric at the same time? Anecdotally, when the backup heat kicks on, the house warms up pretty fast (maybe 2°F every 15 minutes)
The backup heat system is electric too: two electric heating elements. One or more of the elements get toggled on when it gets too cold for the heat pump to maintain the internal house temp.
I have noticed recently that when the backup heat is on, the heat pump compressor is still running, even when it is super cold out (like 0°F). Is that normal?
I want to add a level 2 electric vehicle charger to my home, but the electrician says that I can't because it would just nudge the "calculated load" of my electrical service connection over the electrical code limit. Having said that, he then said that if the HVAC control system was such that it only turned on either the heat pump OR the backup heat (but never both at the same time) then my service connection would be enough.
He said it was rule 8-106 Subrule 2/3 in Canadian Electrical Code:
Is there a way to tell the controller module to only turn on the backup heat OR the auxilliary but never both at the same time?
The control system is a Honeywell THX9421 Prestige IAQ with EIM
Looking at the manual for the control system, it says on page 100 that there are backup heat types that allow you more fine-grained control over how backup heating works.
For example, it looks like instead of selecting "electric forced air" as the backup type, the installer could have selected "other" as the backup type and then selected whether or not the backup heat was allowed to run with the heat pump (custom configuration).
Sounds like I might just need to "educate" the HVAC contractor about this possibility and get him to come and re-program my thermostat? Does that sound right? And then my electrician can change his load calculation and save me the 3 kW of the heat pump?
Is there a reason why it would be bad to not run both heat pump and backup electric at the same time? Anecdotally, when the backup heat kicks on, the house warms up pretty fast (maybe 2°F every 15 minutes)