What size was the old A/C, and what size is the new A/C.
Were you using the attic fan last year? It could be drawing conditioned air from teh house into the attic. If it is, then the conditioned air is being replaced with high humidity air from the outside.

Is your duct work in the attic?

May have a leaky return or supply if it is.

Does your furnace have a VS blower.
 
Set the fan to auto.

Set to on, the humidity raises once the outdoor unit shuts off.
Next, most likely your old air handler was not moving 400 CFM per ton. And your contractor probably has the VS set for 400 CFM per ton.
Have him set it to 350 CFM per ton.
And enable comfort r.
 