Hoar Frost, temp fixes?

I just did a search for "high efficiency furnace venting frost" I found alot of people have / had the same problem I am having. I have a High 93% efficient funace, and the intake gets full of frost on the coldest of nights.

I have used a hair dryer to blow backwards to push the frost out. since then I dont think it matters. (I used the hair dryer to push air in the exhaust pipe.)

I have put a ceramic air heater under the venting pipes in side the house, right under the pipes, where the PVC exits the house.

We (my wife and I) have used a Dryer lint filter cleaner, (bristle flexible brush that can be used to get the lint bunnies out of the dryer for the longer dryer filter types.

What every we choose to do, we have to cycle the power to get immediated (with in 15 minutest) reset cycle. Since it takes 15 minutes, (I will get distracted, and that 15 minutes gets extended by hours.) Would it make more sense to put a inferred heater next to intake pipe, or wrap that pipe with heater tape?

Problems since installed 2002 Feb.

Tobie
 
Hoar Frost, temp fixes? got it fixed

Sorry about hijacking, in my previous msg I stated the Hoar frost issue. I found the book, and discovered that the HVAC technicians reversed the PVC tubing. The Intake air is suppose to be the shorter of the 2. Just a elbow bent down. The Exhaust can be longer. due to hotter than ambient temp. so that crystals/hoar frost will not form on the longer tube.

Hope this helps.
Tobie

Instructions, why didn't my HVAC techs read it to begin with????
 