Heil (carrier/bryant/icp, etc) ion communication issue

1.7K views 9 replies 4 participants last post by  Lukengruven  
Having trouble with the ion thermostat finding the indoor unit. Any one have any suggestions?
New install
2024 heil g80ctl (w/nfc)
Ion syst0101cw thermostat
2.8vdc between dx+ / dx-
28vac between R & C
123.8 vac supply voltage
The green com light lights but does not blink
Thinking furnace board might be the culprit do to low communicating voltage.
I have calls into the supplier.
Any suggestions would be welcome.