HVAC-Talk: Heating, Air & Refrigeration Discussion banner

Heat pump pump down

1 reading
16K views 25 replies 15 participants last post by  Mr Breeze84  
#1 ·
Hey fell!

This may be a silly question for some, but we are in SoCal and rarely see heat pumps let alone heat pumps with a stuck TXV right out of the box.

The system and refrigerant inside of it are brand new right now I would like to keep the refrigerant in the system by pumping it down so we can change the TXV. But we cannot pump it down in cooling because of the stuck TXV

Is there a Safe way to pump a 4-ton residential down in heat pump

Goodman 4-ton 14 SEER
 
#2 · (Edited)
If TXV ( indoor section ) is not opening in cool mode wouldn’t that be the same as closing off the LLSV. Thinking you just need to make sure RV is always energized and never deenergize while pumping it down in cool. If it has a LPC, may need to jump out, as that will drop out RV and shut system down. Also who’s to say your going to get the total charge in the outdoor unit especially if your lineset is on the longer side. Don’t believe your suppose to pull into a very low suction pressure with a scroll compressor also, unlike a recipercating compressor.

Is the indoor TXV adjustable? Yea maybe unable to pump down if the TXV is a hard shut off during cool? I always thought you still get a little seepage no matter what?
 
Save
#9 ·
I think it best to recover it all and weigh in the whole charge on a heat pump. Again I think he's talkin about the outdoor TXV. Why save PART of it and have to extrapulate the rest? new unit there should be an allowance for you to cover the cost associated, drier, r410a,etc. labor allowance as they're called are never ment to "pay you" only help you recover some of your expenses. Or just see if you can get another unit, your client would feel better about that.
I see why he wishes to "save" the charge, HP could have 14-16 lbs iin it.
 
#10 ·
I’m willing to bet they welded the copper without flowing nitrogen...all that ash trash is floating around inside...seen it too many times...
I always recover with a catch all filter dryer and then reinstall the refrigerant with it on..
 
#11 ·
One word of warning here. You need to make sure that the valve will hold pressure backwards when pumping down in heating. Trane had a ball valve on the gas line that would hold pressure in the condenser but when trying to pump down in heating it would not hold the pressure and push the ball out of the socket so you could not turn the valve to open it either.
 
Save
#15 ·
Pumping a HP down in heat mode is virtually the same procedure as in cool made. You close the liquid line port off & when you think its pumped down enough you close the big line port. The biggest difference is you usually can't get all the gas out like you can when pumping down in cooling but you can get most of it. You probably need to bypass a pressure switch too. Sometimes it's not worth the hassle if you still have to recover what's left in the condenser or if you want to put a dryer outside the unit too.
 
Save
#17 ·
@ Garyed

Do I mis understand? If in AC its close, liquid first then suction when satisfied, in heat pump mode wouldnt you do the opposite for heat pump? Shut gas side first then shut liquid line last since its in the reversed flow / state of AC?
 
#19 ·
@ Garyed

Do I mis understand? If in AC its close, liquid first then suction when satisfied, in heat pump mode wouldnt you do the opposite for heat pump? Shut gas side first then shut liquid line last since it’s in the reversed flow / state of AC?
After 3 years
 
#24 ·
My question.... for whatever reason...I've never attempted to pump down a heat pump to the condenser in heat mode. I always energize RV (except Rheem and ruud) and pump down that way.

I thought I was understanding that some of you do a pumpdown to condenser without energizing the RV and leaving it in heat pump mode.
 