As an owner's HVAC contact person, I'd like to bring up that we have 2 building projects in the planning stages, out of eventually 5-6 "large" municipal buildings to eventually change out TAC, Andover, and Trane legacy controls to LON bus field controllers and Ethernet connected supervisory controllers.
Two legacy DDC buildings (one JACE each) already have an R2 overlay on top of the legacy systems with a server in between them. The next buildings to get upgrades can start from scratch, by replacing rather than integrating the obsolete legacy controls. These will be our first non-legacy field controller projects.
In our location, we have a Johnson branch (strictly Metasys), TAC (R2), fairly close by, and Honeywell (R2 & AX) and Johnson ABCS(FX-40 NiagaraAX) are about twice as far away from our location.
I'm told that an engineer has been hired for (new chiller/boiler/AHUs/DDC) one of these two projects with the understanding that the DDC system(s) is to be "open" either Bacnet or LON AND have similarities in operation and maintenance to our two existing R2 overlay-legacy controller buildings.
In researching competative bidding for the control replacement portion of the work, I found a Section 15900 spec on a site where the intention of the spec is stated to be a Niagara head end and LON field bus, no proprietary protocols between field controllers. The boilerplate (no control sequence included) is accessed by going to http://www.hvacc.net/ and clicking on the FMCS Spec 15900 button.
Will this spec allow Metasys NAE network area controller to compete as well as Niagara AX or R2? If Metasys (NAE or other network controller) meets the spec, are the NAE head-ends equivilent to Niagara (R2, AX JACE, Johnson FX40 -- and PC supervisor) ?
NAE pdf under Metasys System/ at :
http://cgproducts.johnsoncontrols.com/default.aspx
Two legacy DDC buildings (one JACE each) already have an R2 overlay on top of the legacy systems with a server in between them. The next buildings to get upgrades can start from scratch, by replacing rather than integrating the obsolete legacy controls. These will be our first non-legacy field controller projects.
In our location, we have a Johnson branch (strictly Metasys), TAC (R2), fairly close by, and Honeywell (R2 & AX) and Johnson ABCS(FX-40 NiagaraAX) are about twice as far away from our location.
I'm told that an engineer has been hired for (new chiller/boiler/AHUs/DDC) one of these two projects with the understanding that the DDC system(s) is to be "open" either Bacnet or LON AND have similarities in operation and maintenance to our two existing R2 overlay-legacy controller buildings.
In researching competative bidding for the control replacement portion of the work, I found a Section 15900 spec on a site where the intention of the spec is stated to be a Niagara head end and LON field bus, no proprietary protocols between field controllers. The boilerplate (no control sequence included) is accessed by going to http://www.hvacc.net/ and clicking on the FMCS Spec 15900 button.
Will this spec allow Metasys NAE network area controller to compete as well as Niagara AX or R2? If Metasys (NAE or other network controller) meets the spec, are the NAE head-ends equivilent to Niagara (R2, AX JACE, Johnson FX40 -- and PC supervisor) ?
NAE pdf under Metasys System/ at :
http://cgproducts.johnsoncontrols.com/default.aspx