We lost power yesterday, so this morning I rented a generator and wired up the 110 bypassing the switch on the side of it. The blower motor turns on when I turn my thermostat to on for fan, but it will not heat. The control board just blinks constantly. Any help would be appreciated.
 
Probably not properly grounded/bonded, or your generator isn't generating clean power. If it doesn't work when your back on street power, you probably smoked something with a power surge.
 
Many furnaces have a "slow heartbeat" blink showing they have power. A "fast heartbeat" indicates a call for heat.
There are intermittent blinks for fault codes.
Are you sure the furnace is receiving a call for heat?
 
Save
We are not allowed to give technical advice in the AOP forums as that is not the purpose of the site. For a consumer/homeowner, make sure the thermostat is set in heat mode and set above room temperature. Beyond that you'll need to call a technician.
 