Furnace rise temp change after AC upgrade

3.9K views 17 replies 7 participants last post by  shellboy  
#1 ·
Amana furnace (AMVC951155) was installed last year by local large company (my long time service provider). Installed HW Prestige IAQ stat with duct temp sensors. Recently had AC replaced by different company (long time acquaintance, licensed) - Goodman DSXC16048 with Goodman CAPT4961 cased coil with integral TXV. Installer removed old 5 ton R22 uncased coil and shortened plenum to acommodate new cased coil. Plenum and old coil were not insulated. New cased coil is insulated. Since it is late season, I had to recently turn heat on and noticed that furnace rise temp is now about 7-8 degrees lower now, in both low fire and high fire. Return and supply temp probes did not move and supply probe is about 6 feet downstream from plenum (equipment in basement with all metal ductwork). No change to blower speed. I would have guessed the insulated coil would have retained more heat and possibly caused slightly higher rise temp, not lower. Is this typical? It seems I have lost 10%+ of my heating BTUs to somewhere. Temps measured after 15-20 minutes. For last year, rise temps have varied no more than + or _ 1 degree.
 
#3 ·
I had ductwork improved when furnace was installed last year to reduce static. After furnace install it was less than 0.3 in low fire at 1265CFM and less than 0.6 in high fire at 1822CFM (with old dry coil), so I don't think airflow changed, but logically you would think that.
 
#5 · (Edited)
The static numbers I quoted were measured with the new furnace but the old coil. The measurements were taken with a probe on the blower side of the media filter and through a hole in the furnace below the heat exchanger. The hole was where one of the safety switches goes. The switch was reinstalled afterwards. The ductwork is large but the restriction had been primarily on the return. Added additional return and two 5" media filters. Was quite pleased with the new furnace during the last year. Limped through the summer with the leaky 20 yr old AC, but decided to replace the 5 ton with a 4 ton 2-stage, because I was so pleased with the 2-stage furnace. Just trying to figure out why the temp rise dropped with the new 4961 coil. Don.t have a manometer to measure static with new coil but guess it could be higher than old coil, especially wet. Have called furnace installer to come check everything while still within my 1 year install labor warranty.
 
#10 ·
So it would seem that regardless if the static went up or down (within reason), then the ECM blower should maintain the same airflow from one coil to the next.

Assuming the gas flow and air flow remained constant, but the duct sensor reads a lower temp, then the heat got lost on the way to the duct sensor.

Would the new larger coil (and/or refrigerant) be absorbing the heat (more heat), than the old coil?
 
#11 ·
I just love it when people give information out sparingly so who ever is trying to help is always wrong. is it variable speed or an x-13 motor? In my opinion if an x-13 motor and lower restriction evap coil then air flow can increase and give you a lower temp rise.
 
#15 ·
I agree that seems to be the obvious answer, but with an ECM variable speed blower, where is the 'more air' coming from?

I am having the furnace installer come tomorrow to check gas pressures. I have had the furnace for 11 months and had two lockouts occur, with otherwise stable rise temps. The lower temp rise was exactly coincident with evap coil change. I'm baffled. On the other hand, without the duct temp sensors, I would be aware at all.
 
#18 ·
I had the installing company come out and check the furnace and gas pressure.

Backstory: When I had the furnace installed last October the high fire temp rise was 58 degrees and the low fire temp rise was 71 degrees (acceptable range 45-65). The gas pressures were not checked by installer (first mistake). I asked for the tech manager to come and check out install and address the high temp on low fire. I suggested that with a variable speed blower ECM blower, the high and low temp rise should both be 56 degrees. per Amana Technical Manual (available online), so it seemed like the gas pressure was high. Without actually checking gas pressure, he lowered the low fire gas setting to get 56-57 degrees and checked static on low fire (0.27) and high fire (0.57). Things were fine until replacing AC this year (see details in OP).
During this week's installer visit everything looked good with pressure switches when investigating two previous lockouts (suspected maybe water in signal hose that activates gas valve, as igniter would glow but no gas flow on last lockout). Checked gas pressures (first time actually checked). High fire was 3.52, pretty much right on. Low fire was 1.61. It was reset to 1.9 spec. Low fire rise temp is now 54 degrees and high fire is 53. From tech manual, target temp is 56. Close enough. Appears that new coil lowered static (did not re-measure unfortunately) and increased air flow which WAS NOT compensated for by the variable speed ECM blower motor, as you might expect. I think I understand that issue, but will address in a separate thread.
 