I had a contractor plug a furnace burner orifice with Teflon tape and rearrange the burners. How serious is an issue like this?
You need to find a different service provider.The reason for plugging the burner orifice on this was because the furnace was tripping limit switches. The contractor believed the furnace was oversized for the house. During this phase of operation, the furnace began to go from the blower cycle to the igniting phaze, then gas shut off, then ignite again repeatedly. Could this have taken a toll on parts and wear and tear?
The reason Teflon tape was used because the tech didn't have an brass plugs on him and said it was temporary but never bothered coming back to do it correctly.
Multiple limit failures, the same one or different ones? Then he replaced the board and ignitor?By the way, this was a Tappan natural gas furnace. The tech only took responsibility for replacing the limit switches 5 or 6 of them, the control board, and ignitor and denies that he touched the burners or plugged the burner when I was standing right next to him when it was performed.
The tech that actually got everything in running safe order again said it was misfiring and gas was also stuck in the chambers. Repeatedly, I'd hear a poof sound when firing up prior to returning to safe operation.
Post the #'sMultiple limit failures on different ones. Then we turned the furnace on after those were replaced and the ignitor turned on and blew up with sparks and all. Replaced the ignitor, still didn't run correctly, then found out the control board was fried.
Finally after all these parts, it turned on but kept tripping switches. His temporary resolution was plugging one burner with Teflon tape and returning but never did.
The tech that found the gas building up in the chamber was a new tech. Combustion analysis done and operating as it should.
This has a metal vent pipe.
In my opinion yes. This is a clear indication that he is worried about his actions.The tech that plugged the burners sent a refund for the entire job.. is what he did wrong here ?
You have a potentially dangerous setup and should shut the system down until a different contractor who actually knows how to use a combustion analyzer for troubleshooting can be contacted and thoroughly go through this unit.Finally after all these parts, it turned on but kept tripping switches. His temporary resolution was plugging one burner with Teflon tape and returning but never did.
That, like all the other fixes he tried, is not only bad for the system, but just puts a band-aid on the problem.Forgot to mention the same tech that plugged the burner orifice also said to run the furnace filterless.