ok. curious what you guys think
typically if i install a new unit and the condenser has a pre- charge (mainly ductless units but guess it could apply to any pre- charged unit) i am a true believer not to pressure test with nitrogen as to not contaminate with non condensables due to valves leaking by or venturi effect.
in the process now of evacuating several ductless units and using vacuum pump for leak checking
the way i see it. if after ive reached 500 or less on micron gauge i shut and valve pump off
if my gauge goes above 1000 after sitting for half hr then i have moisture still in system. if it goes above 5000 then its a leak. usually it withh rise 200 or so microns and stay there
is this as reliable as puting unit under 200 lb nitrogen pressure
typically if i install a new unit and the condenser has a pre- charge (mainly ductless units but guess it could apply to any pre- charged unit) i am a true believer not to pressure test with nitrogen as to not contaminate with non condensables due to valves leaking by or venturi effect.
in the process now of evacuating several ductless units and using vacuum pump for leak checking
the way i see it. if after ive reached 500 or less on micron gauge i shut and valve pump off
if my gauge goes above 1000 after sitting for half hr then i have moisture still in system. if it goes above 5000 then its a leak. usually it withh rise 200 or so microns and stay there
is this as reliable as puting unit under 200 lb nitrogen pressure