Conventional wisdom should not be ignored off-hand

A two stage, 2 ton system has a variable speed blower that has a minimum setting of 1000 cfm. That means that for most of the year, here in Oregon, it will be operating at 750 cfm/ton.

So, can I just disregard those traditional figures (350-450 cfm/ton)?

The high HSPF is what the Oregon Department of Energy wants me to choose.
What is the model number and manufacturer?
I am sure others here would know the recommended setting and unique features.
The numbers mentioned mean that the coil face area has nearly doubled.

What part of Oregon? You must be in a rain shadow( < 20 inches rain/ year).

Those numbers you mention must be MAXIMUM.

Most of us here would not see more than 450 CFM/ton in a manufacturers recommended set-point and only for the driest climates.
 