I'm working on a newer Hussmann parallel rack and under moderate load my drop leg is running consistently 1-5psi higher than the dish charge. This changes when the rack is under a higher load (i.e. higher than 85 or 90 ambient or case just coming out of defrost) I've searched quite a few threads and have found discussions about A8 and A9 adjustments but none of these apply since it all hinges on having higher discharge than drop leg. I agree that this is highly unusual and have exhausted my resources including some very intelligent experienced techs and some highly educated engineers. I'll describe the system starting from the discharge header at the rack. From the header it passes through the oil separator and then enters the heat reclaim valve. Between the separator and the HR valve is the discharge line feeding the A9 valve (solenoid controlled). After the HR valve the line continues 20 vertical feet and about 60 horizontal. To the inlet to the air cooled condenser on the roof. Out of the condenser it returns to the rack and first passes through the A8 then passes through a tee. On the top of the tee sits the vertical surge receiver. After passing under the receiver at floor level it continues to the LL filter drier then sight glass then liquid header. The receiver has a vent line that runs from the top side of the housing to the condenser inlet line at the point where you would place a purge valve. There is a check valve in the vent line allowing gas to escape the receiver but not enter. This is a low temp rack running 404a and electric defrost. Floating head based on condenser TD floating suction. The heat reclaim is reheat for the seasons 4. My theory has to do with gravity as it relates to different refrigerant densities. After the condenser the refrigerant is at a higher density than it is when entering this makes it heaver. If you have two pipes, each on their own scale, one is full of water and the other only contains air. Which one exerts more weight or psi on the scale? This is as far as I've gone with this theory. Does anyone have another explanation or something to add that might disprove the gravity theory? This is the root of my issues involving logging all of my refrigerant in the receiver and only leaving a small river of liquid in the liquid line. Note: when I close the vent line from the receiver to the condenser my receiver drains enough to give me a solid column of liquid. This is significant because it enters the condenser piping where the condenser line goes horizontal after the vertical riser. This could be an area of lesser pressure than what's at the bottom in the liquid filled receiver. This also spells a possible issue with low velocity in condenser piping?