Humidity question. Need advice!
(Quick summary: House humidity was fine, but air handler closet was 75%RH, growing mold. After putting small dehumidifier in A/C closet, the closet is better, but the rest of the house is 70%RH)
My air handler is in a closet in the hallway. We noticed the air handler closet would stay around 75% humidity (even if the rest of the house was consistently around 50%). The RH in the closet went even higher when the A/C was running--we were getting mold on the wall inside that closet.
We got all the ducting replaced last month (for different reasons), and while everything was opened up, we discovered the old furnace flue was never sealed---so it was allowing tons of outside/attic air to be pulled into the air handler. We got that sealed up, which we thought would fix the humidity issue. But the closet stayed humid.
This week I put a small, standalone dehumidifier in the A/C closet (I had discussed the idea previously with the HVAC guy who did our ductwork). The dehumidifier is successfully keeping that closet around 50%RH (it is running nearly constantly, but the volume of water seems to be low). But now the rest of the house is at around 70%RH! So the closet is better, but now the house is worse than ever! I'm wondering if the dehumidifier is changing the air going into the air handler, which is affecting the efficiency of the A/C. Could it be that the A/C is not working correctly (the air is sure cold)?
Is a dehumidifier near the air intake a good idea? Are there any other variables I could change to help narrow down the root issue?
I'm not sure who to call. Some friends recommended an energy efficiency specialist to look at the whole house---or should I call an HVAC pro first?
Notes & extra info:
1-story, 1400 sq ft house; no subfloor; flat roof with very little attic space (no crawl-space); ducting is above a dropped ceiling. Located in Florida (very humid outside year-round). The house was built in 1950s originally without HVAC. The air handler closet is in the hallway, and that closet door is the only return in the house. There are no vents in the hallway (so the hallway air is theoretically more stale). The whole HVAC system was replaced June 2017. Then we had all the ducting replaced (with flex duct) in December 2018 and made sure to seal off spots where outside air was coming in. There is no room in that small closet nor in the attic for a whole-house dehumidifier.
Not sure what to do from here. My wife has health problems, and the humidity/mold-risk needs to be resolved.
Thanks for your time!
(Quick summary: House humidity was fine, but air handler closet was 75%RH, growing mold. After putting small dehumidifier in A/C closet, the closet is better, but the rest of the house is 70%RH)
My air handler is in a closet in the hallway. We noticed the air handler closet would stay around 75% humidity (even if the rest of the house was consistently around 50%). The RH in the closet went even higher when the A/C was running--we were getting mold on the wall inside that closet.
We got all the ducting replaced last month (for different reasons), and while everything was opened up, we discovered the old furnace flue was never sealed---so it was allowing tons of outside/attic air to be pulled into the air handler. We got that sealed up, which we thought would fix the humidity issue. But the closet stayed humid.
This week I put a small, standalone dehumidifier in the A/C closet (I had discussed the idea previously with the HVAC guy who did our ductwork). The dehumidifier is successfully keeping that closet around 50%RH (it is running nearly constantly, but the volume of water seems to be low). But now the rest of the house is at around 70%RH! So the closet is better, but now the house is worse than ever! I'm wondering if the dehumidifier is changing the air going into the air handler, which is affecting the efficiency of the A/C. Could it be that the A/C is not working correctly (the air is sure cold)?
Is a dehumidifier near the air intake a good idea? Are there any other variables I could change to help narrow down the root issue?
I'm not sure who to call. Some friends recommended an energy efficiency specialist to look at the whole house---or should I call an HVAC pro first?
Notes & extra info:
1-story, 1400 sq ft house; no subfloor; flat roof with very little attic space (no crawl-space); ducting is above a dropped ceiling. Located in Florida (very humid outside year-round). The house was built in 1950s originally without HVAC. The air handler closet is in the hallway, and that closet door is the only return in the house. There are no vents in the hallway (so the hallway air is theoretically more stale). The whole HVAC system was replaced June 2017. Then we had all the ducting replaced (with flex duct) in December 2018 and made sure to seal off spots where outside air was coming in. There is no room in that small closet nor in the attic for a whole-house dehumidifier.
Not sure what to do from here. My wife has health problems, and the humidity/mold-risk needs to be resolved.
Thanks for your time!