Does the air conditioning system have a CPR valve? I know CPR valve is an option in refrigeration system, but have no idea whether it is necessary in vehicle A/C or home used A/C system.
You are correct in that a CPR is used to limit compressor load, however it is not done by hot gas bypass (HGBP). The CPR is simply a pressure regulating valve installed in the suction line upstream of the compressor which throttles closed on a rise in outlet pressure...ie, compressor suction pressure.Used in refrigeration during start-up to limit compressor load. Basically a hgbp from discharge to suction.
Problem is getting everyone to uses the same book. ASHRAE book is only 140 pages and is supposed to be the industry standard. I remember when R-400 series refrigerants were being promoted in the early '90s, they had no definition for heat exchanger approach with a refrigerant glide, just found a 2006 email correspondence with ASHRAE where they were finally trying to settle on an official definition. Copeland was not using the same standard of most refrigerant manufactures at that time & ARI also was lacking information.In my copy of "HVAC/R Terminology"- A Quick Reference Guide by Richard Wirtz, 364(+-)pages.
It is a Good Read (reference-like a Dictionary)