Okay, was doing some pms and keep coming across AC units with low boiling points in evaporator 27 degrees with high SH 35. Added R22 got SH down to target using WB return condenser entering air dry bulb chart but boiling point stayed at 27/28 degrees. I thought from my schooling the saturation temp should be around 40 degrees ideal. My trainer said it was because of air flow issues etc(not enough heat load on evap). I was thinking about this and thought the fixed orifice would cause the pressure drop so its temp would be 40 degrees without any air acting on evap coil. The heat load varies the superset but would have very little effect on boiling point temp because most is latent heat of vaporization then SH is added which might increase pressure a little but not a lot. This unit is a fixed orifice. I am figuring either it is a restriction in orifice (to much pressure drop), not sized right, etc. Also, high side pressure was 188psig and outside temp was only 76 degrees. Any nuggets of wisdom will be really appreciated. Starting to get charging down on systems that run probably now just slowing learning the thousands of variables that effect those important SH and SC numbers.
Thanks,
Thanks,