I have a stumper... went on a call for no cooling on a old York split. Found the compressor tripped on high head. Found that the condenser fan is running only half speed. Checked capacitor and it was spot on at 15MF and amp draw was spot on too at 1.5 amps. Also checked voltage which also was fine at 460 volts. Figured the motor must be bad so I replaced it along with the capacitor. Also replaced the three pole contact see it was extremely pitted.
Now here is the kicker. The new fan is doing the same thing. Amp draws, capacitor and voltage are all spot on. Power in is three phase and the condenser fan is single phase using two of the legs. Checked three phase power in and all three legs are good. I also pulled the wires to the tandem compressors and only ran the fan and still half speed. Even OHMed all the wires to the fan motor and they were fine.
What am I not seeing....
Now here is the kicker. The new fan is doing the same thing. Amp draws, capacitor and voltage are all spot on. Power in is three phase and the condenser fan is single phase using two of the legs. Checked three phase power in and all three legs are good. I also pulled the wires to the tandem compressors and only ran the fan and still half speed. Even OHMed all the wires to the fan motor and they were fine.
What am I not seeing....