R-22 System. System is off. I put my gauges on the line then turn the system on. Pressure is 60/225. Allow the system to run 10 minutes. Suction line temp is 43. Pressure remains constant at 60/225.
So, I do my superheat calc .... 43 (suction line temp) - 36 (evap coil temp for R-22 at pressure of 60) = 7 Superheat.
Then, as a newbie, what throws me for a loop is that the suction line temp slowly declines from 43 down to 36 as the system continues to run for another hour. Pressure still remains constant at 60/225.
So, is my superheat 7, or 0 ???
Thanks.
So, I do my superheat calc .... 43 (suction line temp) - 36 (evap coil temp for R-22 at pressure of 60) = 7 Superheat.
Then, as a newbie, what throws me for a loop is that the suction line temp slowly declines from 43 down to 36 as the system continues to run for another hour. Pressure still remains constant at 60/225.
So, is my superheat 7, or 0 ???
Thanks.