Chiller York YCAA B 170, system no.2 tripping on low suction

1 reading
9.5K views 26 replies 5 participants last post by  altaf22m  
#1 ·
Can any one tell me what can be the reason of low suction pressure in York chiller model YCAA-B-170. After descaling the three BPHE COOLER of the three chillers they runs for one month with healthy suction pressure 65 to 75 psig, but slowly one by one the chiller suction pressure starts getting low, now it's goes up to 35 to 45 psig. This chillers are used for cooling air compressor systems. There is no water flow in and out is given on cooler, but instead given on chilled water pump discharge going to air compressor heat exchanger and the warm water coming back to chiller in main header. The pump discharge water is showing 37 psig and chilled water inlet header pressure to inlet of cooler is showing 10 to 12 psig. The chilled water is treated with anti freeze coolant. The reason for descaling cooler was scale formation as it was tripping on antifreeze thermostat. After descaling the problem was solved, but after one month it starts lowering the suction pressure. For your info, the outlet of chilled water goes to 5000 liter of insulated water tank, and from tank the chilled water goes to suction of pump, the suction line filter of pump is also checked foun clean. But still problem not solved the flow of water on flow meter is same healthy as usual i.e 129 gal/min. Please guys your comments please if any body face similar problem.
 
#2 ·
Is this chiller on R407C refrigerant? Are your sensors good and transducers good?
Has the refrigerant ever been removed from the system and then reused back into the system?
You mention three chillers, are they all showing the same symptoms?
 
#4 · (Edited)
Yes, it's R407C refrigerant, and we have three chillers "A " "B" and "C" having two circuits, system no.1 and system no.2.
Before this issue, the chiller "C" was tripping on antifreeze thermostat, as evaporator temperature was reaching 30 degree Fahrenheit, this 30 degree Fahrenheit was reaching only when system no. 2 starts. Rest of other two chillers "A" & "B" were performing well.

As I found, evaporator was scaled, I did the Descaling on the heat exchanger using rydlyme chemical by heat exchanger servicing professional, and then found the system was performing well, no more trip on antifreeze thermostat. And suction and discharge pressure was well maintaining. Delta T Between the cooler inlet and outlet was 14 degree Fahrenheit at full load conditions of chiller.

As we found, the result has been improved after descaling evaporator heat exchanger, we did the Descaling on other two chillers also, as this chillers were 16 years old and it was descaled before also three years back.

After 45 days of Descaling heat exchanger, it was observed that one of the chiller "C" system no.2, discharge pressure is 175 Psig , suction pressure going below 45 psig and now it's going up to 33 psig and tripping on low suction pressure at 29 psig after running for two hours or it trips after half an hour if ambient is 69 degree F.
And outlet of expansion valve and suction line
started icing up.

There was no leak in system, system was flushed with R141B & NITROGEN, filter drier & Txv valve of same size was replaced with new one but still same problem.

And, after this chiller "C" issue some two months passed away and the same problem started for chiller "A" & "B" also. Now, we have to kept one compressor off to prevent low suction pressure.

Note: This chiller has two compressors on system no.1 & two compressors on system no. 2.

On all three chillers "A" "B" and "C' System no.1 pressure is healthy suction pressure 60 to 70 psig.

And system no.2 is only affected on all three chillers. Why?

Chilled water line strainers cleaned, and checked water flow found normal 122 gal/min.

Now, with three compressors running Delta T is 6.5 degree F accross heat exchanger.

Superheat at system no.2 is 3 degree Fahrenheit.
And subcooling is 5 degree F.

Superheat at system no.1 is 16 degree Fahrenheit and subcooling is 10 degree F.
 
#3 ·
That is quite a tough question to answer without the following info.

Refrigerant type
Is there a fine mesh strainer at the entrance of the exchanger?
Entering and leaving water temp
Pressures
Superheat

If you had issue with the exchanger getting clogged I'd say follow the manufacturer recommendations and install a fine mesh strainer at the chiller entrance.
A good water treatment help a lot for plated heat exchanger
 
#5 ·
Yes, it's R407C refrigerant, and we have three chillers "A " "B" and "C" having two circuits, system no.1 and system no.2.
Before this issue, the chiller "C" was tripping on antifreeze thermostat, as evaporator temperature was reaching 30 degree Fahrenheit, this 30 degree Fahrenheit was reaching only when system no. 2 starts. Rest of other two chillers "A" & "B" were performing well.

As I found, evaporator was scaled, I did the Descaling on the heat exchanger using rydlyme chemical by heat exchanger servicing professional, and then found the system was performing well, no more trip on antifreeze thermostat. And suction and discharge pressure was well maintaining. Delta T Between the cooler inlet and outlet was 14 degree Fahrenheit at full load conditions of chiller.

As we found, the result has been improved after descaling evaporator heat exchanger, we did the Descaling on other two chillers also, as this chillers were 16 years old and it was descaled before also three years back.

After 45 days of Descaling heat exchanger, it was observed that one of the chiller "C" system no.2, discharge pressure is 175 Psig , suction pressure going below 45 psig and now it's going up to 33 psig and tripping on low suction pressure at 29 psig after running for two hours or it trips after half an hour if ambient is 69 degree F.
And outlet of expansion valve and suction line
started icing up.

There was no leak in system, system was flushed with R141B & NITROGEN, filter drier & Txv valve of same size was replaced with new one but still same problem.

And, after this chiller "C" issue some two months passed away and the same problem started for chiller "A" & "B" also. Now, we have to kept one compressor off to prevent low suction pressure.

Note: This chiller has two compressors on system no.1 & two compressors on system no. 2.

On all three chillers "A" "B" and "C' System no.1 pressure is healthy suction pressure 60 to 70 psig.

And system no.2 is only affected on all three chillers. Why?

Chilled water line strainers cleaned, and checked water flow found normal 122 gal/min.

Now, with three compressors running Delta T is 6.5 degree F accross heat exchanger.

Superheat at system no.2 is 3 degree Fahrenheit.
And subcooling is 5 degree F.

Superheat at system no.1 is 16 degree Fahrenheit and subcooling is 10 degree F.

Water treatment done by our mechanical department and found pH level above 6.
 
#6 ·
If the problem is found on all three chiller I'd say it might be a water loop problem.

When you say that you have 122 gal/min, is flow per chiller or for all three chiller?

How do you measure the flow?
If it's a gmp meter is it accurate?

Like I said in the previous reply, plated heat exchanger are really sensible to clogging if the manufacturer reccomandations are not followed.
The ask for some specific parameters to be maintained on the water side.
It is mandatory to have a fine mesh filter at the chiller entrance.

You can try to do a counterflow flush at the heat exchanger to remove any trapped particules.

Envoyé de mon SM-A715W en utilisant Tapatalk
 
#27 ·
Hi Patpinet,

The problem is solved by replacing all the 3 BPHE COOLERS, and the chillers are performing well. Looks like coolers were internally clogged and loose efficiency due to ageing. Thanks all for exchanging your ideas and efforts. :)
 
#11 ·
Evaporator approach is 5 degree F with 75 % load. Only three compressor kept running. Compressor no.4 kept off to maintain suction pressure on system no. 2, if we run compressor no. 4 , system no. 2 trips on low suction immediately.
 
#10 ·
Evaporator approach is 5 degree F with 75 % load. Only three compressor kept running. Compressor no.4 kept off to maintain suction pressure on system no. 2, if we run compressor no. 4 , system no. 2 trips on low suction immediately.
 
#13 ·
Can you fill a complete log sheet with pressure and everything.

I believe a YLAA log sheet can work out for you.
Take the flow measure at the chiller with pressure drop.

I'm not familiar with your specific chiller but I'm on jci site looking for info


Envoyé de mon SM-A715W en utilisant Tapatalk
 
#22 ·
If all three chillers are experiencing the same fault, the problem is with the system that is common to all machines.

make sure your glycol solution is the correct concentration. if it's too strong (thick) you will not get the proper flow, due to lack of available pump HP.

also, might be a good idea to inspect your glycol pumps for wear.


not knowing your system, we can just speculate.......

you may have a valve that is not opening, even though you think it is, could have a plugged pump strainer, could have an inline pump failed, etc. etc.
 
Save
#24 ·
Real quick like that I'd say your missing some refrigerant on the circuit 2.
Or its not the right refrigerant.

Do you have a sight glass and can you confirm that it's clear (free of bubble)

If not a clogged heat exchanger is a possibility, but only half of it doesn't make sense
 