Multiple HVAC techs have mentioned that I will need a 40 amp breaker with 10 gauge wiring for a Bosch heat pump (BOVA-36HDN1-M20G). According to the spec sheet the Max. Overcurrent Protection is 45 and the Minimum Circuit Ampacity is 26.3 so the breaker size is less than the max overcurrent protection and the wire size can carry the 26.3 amps. However, according to the Canadian electrical code section 14-104 a 10 gauge wire can have a max. 30 amp breaker. Is there some exception somewhere else in the code that does allow this 40 amp breaker with 10 gauge wire combo for a known load such as an AC or heat pump?
Or are these techs incorrect and I should go with a 30 amp breaker (which is still less than the max overcurrent protection) or upgrade to 8 gauge wire to match the 40 amp breaker they suggest?
Thanks,
Harry
Or are these techs incorrect and I should go with a 30 amp breaker (which is still less than the max overcurrent protection) or upgrade to 8 gauge wire to match the 40 amp breaker they suggest?