Good morning. I have a customer with a Carrier 38MAQB09B-301. The indoor unit is a 40MAQB09B-331. We did not install this unit. The serial # is 0118V*****
No cooling call. Power to the indoor and outdoor units. DC voltage fluctuates at outdoor unit from 5VDC up to 20VDC. Does not go into the negative VDC range at all. Difficult to catch on a digital meter but that's what I see on terminals + and S. Carrier is saying that I need a new circuit board on the outdoor unit and I should also get the board for the indoor unit as well.
Quoted the customer for the parts but I have a nagging issue with something. The condensate pump is running continuously. The pump is installed inside the front cover. The cover is very difficult and damn near impossible to remove to get at this pump. Not much in the way of mention of this pump in the service manual. No fault codes and no display on the indoor unit. The outdoor unit is mentioned in the service literature but I see no LED's or anything up there with the top panel and circuit board panel off.
This unit looks like a real pain in the ass to service and I just have so many concerns that I am taking the right path with this. I would appreciate some input form technicians who are familiar with these units and their service. Do I need to look closer at the pump? I don't think it should be running constantly. Is there a way to remove the cover for service access or are you expected to take the unit off the wall? Where is this indoor circuit board? Is it the one mounted to the inside of the front filter cover?
I have access to all the literature but the instructions are a bit vague and worded in a misleading fashion. I can tell it's translated form Chinese.
I realize that I have a few questions in this initial post but I just can't help but think that I'm missing something on this service call. Perhaps the condensate pump seems as if there is no sending unit and was wired constant or there is a sending unit and the float switch has the S wire open but that should give me an E1 fault. The customer said that there was initially an E1 fault but now there is no fault at all and no display or blinky lights on the indoor unit.
No cooling call. Power to the indoor and outdoor units. DC voltage fluctuates at outdoor unit from 5VDC up to 20VDC. Does not go into the negative VDC range at all. Difficult to catch on a digital meter but that's what I see on terminals + and S. Carrier is saying that I need a new circuit board on the outdoor unit and I should also get the board for the indoor unit as well.
Quoted the customer for the parts but I have a nagging issue with something. The condensate pump is running continuously. The pump is installed inside the front cover. The cover is very difficult and damn near impossible to remove to get at this pump. Not much in the way of mention of this pump in the service manual. No fault codes and no display on the indoor unit. The outdoor unit is mentioned in the service literature but I see no LED's or anything up there with the top panel and circuit board panel off.
This unit looks like a real pain in the ass to service and I just have so many concerns that I am taking the right path with this. I would appreciate some input form technicians who are familiar with these units and their service. Do I need to look closer at the pump? I don't think it should be running constantly. Is there a way to remove the cover for service access or are you expected to take the unit off the wall? Where is this indoor circuit board? Is it the one mounted to the inside of the front filter cover?
I have access to all the literature but the instructions are a bit vague and worded in a misleading fashion. I can tell it's translated form Chinese.
I realize that I have a few questions in this initial post but I just can't help but think that I'm missing something on this service call. Perhaps the condensate pump seems as if there is no sending unit and was wired constant or there is a sending unit and the float switch has the S wire open but that should give me an E1 fault. The customer said that there was initially an E1 fault but now there is no fault at all and no display or blinky lights on the indoor unit.