Have one month old Carrier Infinity System with variable speed 5 stage heat pump (25VNA8), fan coil (FE4AN) and Infinity programmable thermostat (black). It’s my first HVAC purchase. Am working with contractor who installed to solve two issues. One issue is that, although the thermostat will connect to WiFi as designed, after about 15 minutes it stops communicating to the system and the system shuts down. It is running latest firmware version per Carrier. As I don’t need to do remote adjusting, it’s not the most pressing issue at this point.
More important issue is the FE4AN is rated to run with max static pressure of .5 and according to thermostat, it is running at around .83. System error message is “too high, please consider duct or filter change”. Does not seem to matter what stage system is in, stage 5 is only slightly higher pressure than stage 1.
I will try to provide enough information to evaluate situation. Thanks.
It is a 3-ton unit with a media cabinet at fan coil with MERV 13 filter that is 20 x 20, pleated, and 4 inches thick. When you run system without filter, the static drops around .2, to .63. Contractor thinks it is a return issue and as a first effort, put a grille below filter directly on fan coil where return air enters from plenum. Net effect was to lower pressure .04, which wasn’t even a dent. No other testing has been done yet. I was disappointed I allowed him to do that as I had already determined it was not useful. It also caused me to lose confidence in the contractor.
Previous system was a Trane with a single stage 2.5-ton heat pump which was leaking coolant at the 10-year mark. Although warranty had not expired, decided to replace it as summer was upon us. Good news is the house is rather simple, bad news is the problem may be the duct system.
It is a 3 bedroom ranch home with no basement and insulated ducts in the attic which is a storage space. There are 14 supply vents and one central return. The contractor was concerned with sizing down to a 2-ton unit but felt comfortable with a 3-ton because it would modulate down most of the time. The house is only 1500 sq feet and is 40 years old with original ducts. I realize that some may consider this oversizing.
Static pressure aside, the system seems to be working as designed so far. It is quiet (inside and out) and runs most of the time on stage 1 or 2. It does not appear to short cycle. It is also set to dehumidify to 48% and has been doing so in the 80 and 90 degree recent weather. We are in Northern Virginia (Fairfax County).
My primary question is: what needs to be done (tested or analyzed) to diagnose how to lower the static pressure to below .5. All options are on the table, including doing some duct work on the supply or return side. I would like to know ahead of time what is going to work so it is not done diagnosed on a trial and error basis and does not involve unnecessary changes. Thanks to any and all and I hope I am adhering to site protocol with this post
More important issue is the FE4AN is rated to run with max static pressure of .5 and according to thermostat, it is running at around .83. System error message is “too high, please consider duct or filter change”. Does not seem to matter what stage system is in, stage 5 is only slightly higher pressure than stage 1.
I will try to provide enough information to evaluate situation. Thanks.
It is a 3-ton unit with a media cabinet at fan coil with MERV 13 filter that is 20 x 20, pleated, and 4 inches thick. When you run system without filter, the static drops around .2, to .63. Contractor thinks it is a return issue and as a first effort, put a grille below filter directly on fan coil where return air enters from plenum. Net effect was to lower pressure .04, which wasn’t even a dent. No other testing has been done yet. I was disappointed I allowed him to do that as I had already determined it was not useful. It also caused me to lose confidence in the contractor.
Previous system was a Trane with a single stage 2.5-ton heat pump which was leaking coolant at the 10-year mark. Although warranty had not expired, decided to replace it as summer was upon us. Good news is the house is rather simple, bad news is the problem may be the duct system.
It is a 3 bedroom ranch home with no basement and insulated ducts in the attic which is a storage space. There are 14 supply vents and one central return. The contractor was concerned with sizing down to a 2-ton unit but felt comfortable with a 3-ton because it would modulate down most of the time. The house is only 1500 sq feet and is 40 years old with original ducts. I realize that some may consider this oversizing.
Static pressure aside, the system seems to be working as designed so far. It is quiet (inside and out) and runs most of the time on stage 1 or 2. It does not appear to short cycle. It is also set to dehumidify to 48% and has been doing so in the 80 and 90 degree recent weather. We are in Northern Virginia (Fairfax County).
My primary question is: what needs to be done (tested or analyzed) to diagnose how to lower the static pressure to below .5. All options are on the table, including doing some duct work on the supply or return side. I would like to know ahead of time what is going to work so it is not done diagnosed on a trial and error basis and does not involve unnecessary changes. Thanks to any and all and I hope I am adhering to site protocol with this post