Hello,
We are looking at installing a VFD drive for the condenser on a carrier unit. The original motors are rated at 3.5 each with the name plate of 5.5 FLA. We replaced the motors for the VFD application and found out that the motors are drawing 6.2 amps per motor. We put back in the original motors and bypassed the drive. We are still reading a current draw of 6.2 amp. We've had two contractors out and couldn't find anything wrong. We cleaned the condenser coils, checked the charge, and verified the blade pitch.
Has anyone ever seen something like this. The problem is we don't know if this has been an issue for a while etc..... Tried to contact Carrier, just got the run around.
Thanks
We are looking at installing a VFD drive for the condenser on a carrier unit. The original motors are rated at 3.5 each with the name plate of 5.5 FLA. We replaced the motors for the VFD application and found out that the motors are drawing 6.2 amps per motor. We put back in the original motors and bypassed the drive. We are still reading a current draw of 6.2 amp. We've had two contractors out and couldn't find anything wrong. We cleaned the condenser coils, checked the charge, and verified the blade pitch.