Was checking out a Carrier 5 ton package today. Co-worker had found orifice restricted last week and he removed the evaporator header and orifice tubes and installed txv. He said he weighed in charge according to name plate. He went back yesterday and didn't like pressures so recovered some refrigerant. I got call today that unit wasn't cooling. 64 degree supply, 80 degree return, pressures: 85-90 low,320-340 high, 20 degree superheat. Adjusted txv and got 15 degree superheat but txv started hunting. Delta T never changed. Added a couple pounds of refrigerant but didn't help. Possible wrong txv?
TXV: SVE4 CP100...gonna checkon that tomorrow. Though about recovering all refrigerant, pulling vacuum and weighing in charge myself just to be sure it is right. Had a 30 degree condenser split so I cleaned condenser coil, knocked pressures down a little for a little while. Not sure if co-worker cut out orifices when he removed the header, so much solder every where. OK, guess I'm rambling trying to figure this out. If anybody has any suggestions I would appreciate it.
TXV: SVE4 CP100...gonna checkon that tomorrow. Though about recovering all refrigerant, pulling vacuum and weighing in charge myself just to be sure it is right. Had a 30 degree condenser split so I cleaned condenser coil, knocked pressures down a little for a little while. Not sure if co-worker cut out orifices when he removed the header, so much solder every where. OK, guess I'm rambling trying to figure this out. If anybody has any suggestions I would appreciate it.